Fire separation wall between tenants in warehouse
Fire separation wall between tenants in warehouse
(OP)
Hi, I have a project in So-Cal where my client will be occupying about 250K sq ft, of an existing, 500K sq ft bldg. There is already a tenant in there, with mostly storage (S) and some offices (B). My client will have the same occupancy, mostly storage, and some small offices (S/B). Per the Cal Bldg Code (CBC) Table 508.4, no separation is needed between these two occupancy groups. But, in cases like this, i have normally had min. 1 hr walls between two separate companies, under the same roof. If anyone out there is using the CBC/CFC, can you tell me if a 1 hour wall is needed? it makes sense, but looking for a code justification. Thanks.
RE: Fire separation wall between tenants in warehouse
Under the CFC, one-hour fire-resistive barriers could by required under Chapter 23 to separate high-hazard commodities from Class I-IV commodities
RE: Fire separation wall between tenants in warehouse
Then i searched this site, and found the following thread from you, to someone else asking the same exact question: "Actually, look at the other way. Say you have a warehouse filled with bags of ice (Group S-2) and adjacent to it is a Group B occupancy with modular furniture offices, server rooms and the like. The Group B occupancy presents a bigger fuel load than the S-2 so the IBC requires fire-resistive separation to prevent fire extension into the less hazardous area." I can't say i completely understand the logic on this, but at least i have a clue on how the code folks were thinking.