Tube in Tube heat exchanger example problem?

Tube in Tube heat exchanger example problem?

Tube in Tube heat exchanger example problem?

(OP)
I havent done calculations for heat transfer in a long time. The heat exchanger we have is a single tube inside another single tube... the inner is sludge with a Cv of .909 BTU/lb*F the outer is 50/50 water/glycol mix with Cv of .832 BTU/lb*F. I've been told we need 1.77MMBTU to keep the temperature up in the sludge tank. I have to figure out the flow rate of each material so I can size the 2 pumps.... does anyone know of a good example of a similar calculation may be that I can look at? or just help me solve this one? I have the old Q=mCv(T1-T2) but I think that mass flowrate will be good for the 2 amounts it would take if you combined the fluids to transfer heat... thanks for any help

RE: Tube in Tube heat exchanger example problem?

(OP)
I hope I used the right subscript on the C... whatever it is supposed to be specific heat of the fluids

RE: Tube in Tube heat exchanger example problem?

(OP)
oh and glycol is being used to heat the sludge in cooler months... glycol starts at 121F and ends at around 105F (just for example) and the sludge is starting at lets say 85F and ending at 100F target temp... and the exchanger is 100 feet long. The outer tube with the glycol is 8" and the inner tube with the sludge is 6".

RE: Tube in Tube heat exchanger example problem?

(OP)
and the fluids are flowing in opposite directions

RE: Tube in Tube heat exchanger example problem?

USAEng

The heat transferred (Q) is equal so what you should have is

scp(s)(T2(s) - T1(s)) = ṁgcp(g)(T1(g) - T2(g))

where the "s" subscript is sludge and the "g" is glycol. Since you said the fluids are flowing in opposite directions, the temperatures should be reversed (I believe.) Someone will correct me if I'm wrong.

Patricia Lougheed

******

Please see FAQ731-376: Eng-Tips.com Forum Policies: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.

RE: Tube in Tube heat exchanger example problem?

(OP)
I guess it is polypropelyne glycol so the Cp is about .850 BTU/lb*F... also found out that the glycol goes from 175 to about 140 through the exchanger.... anyhow so if we need 1.77MMBTU heat transfer to the sludge would you then need Q=mCp(T2-T1) --> 1.77x10^6=m(.850)(175-140) = 59,500 lb/hr = 123 gal/min... then setting the equations equal to eachother and solving for Ms would be Ms=Mg(8.18)... so 1006 gal/min sludge? I must be missing something unless we were given a wrong number for the required heat input (1.77MMBTU)... those numbers are larger than I thought they would be... but maybe a correct estimate?

RE: Tube in Tube heat exchanger example problem?

You seem to be missing the flowrate or mass related to your 1.77MMBTU. That's an energy quantity, which means that corresponds to some sort of mass*temperature product.

I'm not sure how you managed to balance the units, but you shouldn't have been able to.

TTFN
FAQ731-376: Eng-Tips.com Forum Policies

RE: Tube in Tube heat exchanger example problem?

(OP)
cant I just use Q=mCp(T2-T1) to solve for m since I know Q=1.77MMBTU and know the temp difference from the beginning to end of the fluid? and then that Q can be used to solve the Q for the sludge... Can someone put me back onto the right path? Thanks

RE: Tube in Tube heat exchanger example problem?

I'm confused. If you already know all the information, someone must have already done the calculation, so what's the purpose of this exercise?

TTFN
FAQ731-376: Eng-Tips.com Forum Policies

RE: Tube in Tube heat exchanger example problem?


If the external tube is not thermally insulated it may lose some heat to the surroudings depending on the outside atmospheric conditions.

RE: Tube in Tube heat exchanger example problem?

(OP)
sorry that is confusing... we have an engineering firm that provided us with a heat requirement for the amount of sludge we have of 1.77MBTU. I am just trying to find the mass flow rate so I can help my boss get an estimate size for hp requirements for the pumps

RE: Tube in Tube heat exchanger example problem?


I'd add some % to the heat duty on account of loses. What do you think ?

RE: Tube in Tube heat exchanger example problem?


In any case, what you get out of the specific heat equation is a total mass. You need to have the flow rate, which then determines how long it takes to heat up the sludge

1.77MMBTU/C.p*deltaT = 1.77MMBTU/(0.909BTU/lb-°F * 35°F) = 55634 lb

So, if you have a flow rate of 1 lb/min (which implies the whole process taking 55634 min, i.e., ~1000hr, which is silly, but the equation scales)

(1 lb/min)*(0.909BTU/lb-°F * 35°F) = 559 W of net heat transfer required, so all you need to determine is how fast you want this to happen, and how much you're willing to pay for maintaining the required flow rates and size of exchanger.

TTFN
FAQ731-376: Eng-Tips.com Forum Policies

RE: Tube in Tube heat exchanger example problem?

(OP)
thanks... I can take it from here... no more replies needed

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close