Consequence and Analysis of a Tank Being Overfilled
Consequence and Analysis of a Tank Being Overfilled
(OP)
A client has asked me what happens to a tank if it were overfilled to the point where fluids ran out of the emergency vent. The tank has a self supporting dome roof and the overfill vent would result in about 5 feet of water above the roof to shell joint, almost filling the dome space. The tank is an API 650 design.
I'm wondering if this is familiar to anyone and if so, would appreciate any recommendations on an analysis method or recommended software.
Will the (upward?) pressure on the roof will impose compressive stress on the top angle, and the greatest risk be to the roof to top angle joint. Should we be concerned with the fact the shell has been overstressed (filled past the design liquid level)?
I'm wondering if this is familiar to anyone and if so, would appreciate any recommendations on an analysis method or recommended software.
Will the (upward?) pressure on the roof will impose compressive stress on the top angle, and the greatest risk be to the roof to top angle joint. Should we be concerned with the fact the shell has been overstressed (filled past the design liquid level)?





RE: Consequence and Analysis of a Tank Being Overfilled
If the venting is incorrect, fix it ASAP. You have a disaster waiting to happen. If that roof is actually frangible, it will be a small disaster. If the roof-to-shell joint holds, it could be VERY ugly.
RE: Consequence and Analysis of a Tank Being Overfilled
For a lot of smaller tanks, shell thickness is based on minimum thickness anyway, and the extra 5' wouldn't matter. Check the stresses and see how it compares to the hydrotest stress or the allowable stress for existing shells from API-653.
RE: Consequence and Analysis of a Tank Being Overfilled
Then we plan to calculate the normal forces on the dome due to the hydrostatic load from partial fill of the dome space up to the overflow, and then calculate the resulting overall load on the dome. If that load is less than the maximum load due to the maximum internal pressure, we think the roof would not fail.
This might even be conservative, as the liquid level above the joint results in an outward hydrostatic load on the joint, which should be ‘helping’ the compression ring resist the joint collapse.
RE: Consequence and Analysis of a Tank Being Overfilled
The tank was designed to receive 6 L/s with a 4" inlet nozzle. The overfill nozzle is 4". During a non autorized operation of the water source system, the tank received 60 L/s during night shift for 4 hours. The overfilling protection system was not conected, because the tank is under construction. I'm writing the technical report of what happened. Now, reading your posts, I have another ideas on how to explain it. thanks!.. if you have other comments which were the causes, please, let me know. I would appreciate them.
RE: Consequence and Analysis of a Tank Being Overfilled
When you say "the overfilling protection system was not connected", does that mean that the 4" overfill nozzle was blocked?
David Simpson, PE
MuleShoe Engineering
"Belief" is the acceptance of an hypotheses in the absence of data.
"Prejudice" is having an opinion not supported by the preponderance of the data.
"Knowledge" is only found through the accumulation and analysis of data.