Hello everyone,
I am doing a study on the inductive effects of a 25kV underground transmission line. The purpose of this is to mitigate any induced currents on a power cable running perpendicular to this line. From what I assume, there will be no inductive effects considering the physical layout but nonetheless I will do a calculation anyways. I am assuming to use this formula:
M = [10^-7]*(Iphase)*[2ln(D/d)]
for the mutual inductance.
Then I will use this formula:
V = dM/dt to find the electric field strength at the induced cable surface and thus able to find induced current flowing.
Now, these cables are perpendicular so by maxwell's equations there should be zero induced current in the cable, but just to be safe, what type of grounding methods do you think would suffice?
I am thinking a faraday shield grounded at one end (to eliminate current flow in the cage). This shield will be similar to a substation ground mat placed parallel to grade.
Any thoughts?
Thanks for your time
I am doing a study on the inductive effects of a 25kV underground transmission line. The purpose of this is to mitigate any induced currents on a power cable running perpendicular to this line. From what I assume, there will be no inductive effects considering the physical layout but nonetheless I will do a calculation anyways. I am assuming to use this formula:
M = [10^-7]*(Iphase)*[2ln(D/d)]
for the mutual inductance.
Then I will use this formula:
V = dM/dt to find the electric field strength at the induced cable surface and thus able to find induced current flowing.
Now, these cables are perpendicular so by maxwell's equations there should be zero induced current in the cable, but just to be safe, what type of grounding methods do you think would suffice?
I am thinking a faraday shield grounded at one end (to eliminate current flow in the cage). This shield will be similar to a substation ground mat placed parallel to grade.
Any thoughts?
Thanks for your time