roof fires from PV installations
roof fires from PV installations
(OP)
Has anyone heard of roof fires caused by PV installations? The attached article describes this in pretty good detail. One suggested fix is to unground the dc side of things. This will take some effort to get the National Electrical Code to buy into this since they presently require it to be grounded.
RE: roof fires from PV installations
Wasen't the installation of lightning rods something like put metal rods on a farm house, and connect them to ground (Sort of like you are doing with solar panels)?
RE: roof fires from PV installations
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
Chinese prisoner wins Nobel Peace Prize
RE: roof fires from PV installations
Just though this group might be interested in a real-life case history. Does anyone have any comments on the analysis offered by Mr. Brooks?
RE: roof fires from PV installations
Mike McCann
MMC Engineering
RE: roof fires from PV installations
RE: roof fires from PV installations
And the PV panel has a flammable backing? Seriously? And most wiring insulation just isn't that flammable, since that's got be one of the only two significant construction requirements for wiring; "insulate the voltages" and "don't burst into flames if the wires get too hot."
And why are there multiple faults in this installation? Seems like there's something else that went on.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
Chinese prisoner wins Nobel Peace Prize
RE: roof fires from PV installations
If we're talking residential, cedar shakes are pretty flammable and still common for roofing around here. And plywood burns pretty well.
David Castor
www.cvoes.com
RE: roof fires from PV installations
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
Chinese prisoner wins Nobel Peace Prize
RE: roof fires from PV installations
It's not a cedar shake residential roof. 383 kW. Big box store.
Ground fault current was over 300 A on a #12 wire. Any idea what that does to the insulation and the wire?
There were problems with the expansion joints. See pictures in article.
The PV panels I've inspected don't look very flammable.
I should have posted this on the Electric Power T&D forum but I thought since it involved PVs, this would be the place where it belonged. I was looking for a better alternative to ungrounding the dc side since the NEC doesn't allow that.
Are there any protection people out there? Will a ground fault protection system work where you wrap a CT around the plus and negative leads going to the collectors? I was looking for a solution that would offer better protection than simply waiting for the existing protection to do it's thing.
RE: roof fires from PV installations
RE: roof fires from PV installations
However if what you are talking about is to small wire, with melting insulation, that is a different story.
David is correct, CT's won't work on DC, but there are other current measuring devices that will (metered shunt).
RE: roof fires from PV installations
In a system with a potential 300Amp fault current then a 0.1 ohm resistor (or shunt) would give the detector an obvious error signal, yet allow a smaller 3Amp fault current through, or perhaps sound a lower priority warning.
... at least it sounds like a starting point. There may be demons in that design that I wouldn't think of (not an EE).
Steven Fahey, CET