150 HP; 220Vac; 3ph motor needs to rewind on 575Vac; 3ph??

150 HP; 220Vac; 3ph motor needs to rewind on 575Vac; 3ph??

150 HP; 220Vac; 3ph motor needs to rewind on 575Vac; 3ph??

(OP)
Hi,
If I rewind a motor 150HP, 220Vac, 3ph on 575Vac, 3ph,
how does it affect all the motor characteristics??
  - Power
  - Heat
  - FLC
  - Efficiency
Regards,
Ziko.

RE: 150 HP; 220Vac; 3ph motor needs to rewind on 575Vac; 3ph??

Power: Is supposed to stay since it is determined by mechanical/physical design of the motor. If it is exceeded, certain parts may collapse or will not last, e.g. shaft couplings, key, etc.
Heat: Heat will somewhat be reduced since Heatdissipation = R x I**2
and current will be smaller at 575VAC.
However, there are some Watt power loss increases related to Eddy Current Effect losses (~ Voltage**2) and hysteresis losses (~ Voltage), which are quadratically and linearly directly proportional to the 575VAC voltage, respectively (accross the parallel branch in the motor equivalent circuit). These loss increases are noticeably smaller, than the Heatdisspation above at the motor rated shaft power, since the parallel branch current is much smaller but about constant, i.e. independent of the motor shaft load.
Full Load Amps/Current (FLA/FLC): Will be lower, approximately = (220/575) x FLC
Efficiency: Will be lower than 575VAC design by the manufacturer, since the motor will have bigger dimensions; however, the efficiency will increase with respect to 220VAC since the Heatdissipation or Losses will be smaller.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - PLM and ERP: Their Respective Roles in Modern Manufacturing
Leading manufacturers are aligning their people, processes, and tools from initial product ideation through to field service. They do so by providing access to product and enterprise data in the context of each person’s domain expertise. However, it can be complicated and costly to unite engineering with the factory and supply chain. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close