15 KV switchgear for an ungrounded delta application

Status
Not open for further replies.

troyc

Electrical
Joined
Jan 8, 2011
Messages
1
Location
US
Can someone provide me with or point me to the recommended phase to phase and phase to ground clearances for the uninsultated bussing in 15 KV gear to be used with an ungrounded Delta service? - Thanks
 
I would look in ANSI C37 standards for metal-clad switchgear. At 15 kV, I don't think ungrounded versus grounded will have any impact on the necessary phase spacing.