NEC conduit seal requirements

NEC conduit seal requirements

NEC conduit seal requirements

(OP)
Looking for somebody with a better practical grasp of NEC requirements for Class 1 Div 1 locations than the group I work with. We have two switches within 18" of each other. Under normal circumstances each switch would require its own conduit seal fitting. If both can be reached by a single fitting can we use one common fitting for both switches?  

Joe Hasik,
CSWP/SMTL/MTLS
SW 10 x64, SP 3.0
Dell T3400
Intel Core2 Quad
Q6700 2.66 GHz
3.93 GB RAM
NVIDIA Quadro FX 4600

RE: NEC conduit seal requirements

Hi Joe,

You didn't state the group -- so first, check your switches' or enclosures' literature versus the class, division, and group. Some enclosures or enclosed devices require a much smaller minimum distance to the nearest conduit seal (I'm looking at one that says 2 inches if group B, 18" if group C or D).

If you don't have any special minimum requirement and are proceeding according to the code default, it's only necessary for the seal to be within 18" of each box.  If the boxes are side by side and there is only one 18" conduit running between them, only one seal is needed.  Actually, that conduit could be 36" long with a seal in the center (but that's pushing it).

The purpose is to prevent hot gases (products of explosion) from building a pressure wave that can blow the conduit apart -- so, looking at your conduit arrangement, follow the path of the gases from each box.  If you can travel more than 18" (or whatever the minimum is for your particular box, class, division, and group) without hitting a seal, you need to add one.

Good on ya,

Goober Dave

RE: NEC conduit seal requirements

Oops, for got my code citation:

NEC (2008) 501.1(A)(3) "Where two or more explosionproof enclosures for which conduit seals are required under 501.15(A)(1) are connected by nipples or runs of conduit not more than 36" long, a single conduit seal in each such nipple connection of run of conduit shall be considered sufficient if located not more than 18" from either enclosure."

Goober Dave

RE: NEC conduit seal requirements

(OP)
Dave,

What if both switches are running to a J-box in a single conduit run? See attached. I still need to get with my designer and sort out his intent, he's a bit new to this. Both of the switches shown in the image are sharing a conduit run back to a J-box somewhere else on the skid. Can both of these switches hide behind a single seal, or do we need to do it similar to what he has shown? I understand that we will need a second seal near the box, within 6" according to the manufacturer.  

Joe Hasik,
CSWP/SMTL/MTLS
SW 10 x64, SP 3.0
Dell T3400
Intel Core2 Quad
Q6700 2.66 GHz
3.93 GB RAM
NVIDIA Quadro FX 4600

RE: NEC conduit seal requirements

Assuming "[o]nly explosionproof unions, couplings, reducers, elbows, capped elbows, and conduit bodies similar to L, T, and Cross types..." are being used in the diagram, you still have a potential problem.  Although it appears at first glance something like an M.C.Escher drawing to me, what we can't see is the fitting in the vertical conduit run from the "T" conduit body.  If it is another seal, then technically you are Code compliant although it is a far more complex installation than necessary. If the fitting is something else then you don't appear to have a seal within 18" of the enclosure that requires it in that part of the conduit run. See the last paragraph of 501.15(A)(1).

RE: NEC conduit seal requirements

Yah, the picture is a little hard to comprehend for me -- can't tell what's on the other side of the enclosure or what's above the T body as rbalex pointed out.

If you don't have a complete sketch to post that shows and names all fittings and enclosures, try this:

Start in each "box" that isn't listed in rbalex's first line above.  Travel down each conduit that leaves such a box. If you travel more than the code-required or manufacturer-required distance OR if you reach another box, you've missed a required seal.

Good on ya,

Goober Dave

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close