Indian Point SD

Indian Point SD

RE: Indian Point SD

Here's the link to the NRC preliminary notificaiton: http://www.nrc.gov/reading-rm/doc-collections/event-status/prelim-notice/2010/.  It leads to an NRC ADAMS document (where I've not had success on posting links): PNO-I-10-006.

However, it seems a pretty straight forward non-nuclear transformer explosion.  Unfortunately, those happen with some regularity at power stations (nuclear or non-nuclear) or substations.  They're a pretty spectacular fire whether at a nuclear plant or at the substation in your neighborhood.  But there is no link between them and the nuclear side of things.

Patricia Lougheed

******

Please see FAQ731-376: Eng-Tips.com Forum Policies: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.

RE: Indian Point SD

(OP)
Thanks, but I was looking for details of the cause (If known), transformer type (Dry, liquid), size, etc.

Sounds to me like liquid filled. Wondering about protective relays involved, this type of failure should be rare with proper maintenence and protection.  

RE: Indian Point SD

According to the link it is the "main transformer" otherwise known as "generator stepup transformer".  They don't make dry transformers that big so it's gotta be oil-filled.

=====================================
(2B)+(2B)'  ?

RE: Indian Point SD

True.

All that size are oil-filled.  Fans circulate air across the sets of coolers behind each transformer.  

Used to use PCB's inside as coolant.  Now oil.    

RE: Indian Point SD

Generally, the most frequent cause of transformer fires is a lightening strike.  Protective relaying probably worked fine as it separated the plant from the grid.  

Since they're not a nuclear component, the level of maintenance is pretty much the same whether they're at a nuclear plant, a coal-fired plant, or a local sub-station.  Unfortunately, with deregulation, the level of maintenance of infrastructure has decreased, because no one wants to pay for it.

 

Patricia Lougheed

******

Please see FAQ731-376: Eng-Tips.com Forum Policies: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.

RE: Indian Point SD

(OP)
A DGA is really all you need to do.  

RE: Indian Point SD

Probably a lighning strike or internal fault. If a lightning strike, nothing you can do. You regularly see 3-10 rapid strikes hit a transmission line prior to the protective relay/station class breaker operating. I've seen the MCOV's go with as little as 2 strikes on a 161kV line. For an internal fault, Zogzog is right. If they followed proper testing schedules, they would have seen an imminent failure by DGA.

Kimberly-Clark in Loudon, Tn had such a failure (lightning) about 3 years ago. Burned for three days.  

RE: Indian Point SD

Quote (zogzog):

A DGA is really all you need to do.
Interesting comment.

I find no reason to assume that a nuke plant doesn't sample and trend DGA on their Generator Stepup Unit transformer. Quite the contrary, based on my firsthand experience I would think dga testing is done at least quarterly and trended. There are NEIL and ANI insurance requirements that drive this, among other things.  

You imply that simple DGA testing would have prevented this event. In general, we have to consider:
1 - There are situations when a problem is detected but immediate action cannot be taken based on plant conditions.
2 -  More importantly, not all failures stretch out over a time-frame that allows detection/action through dga.  In addition to lightning mentioned above, there can be through-fault leading to mechanical-induced turn-to-turn fault which can escalate rapidly. There are other scenarios as well...

For this particular event, according to the link, the failure was initiated by a bushing.   If the failure originates inside a bushing without heating the main-tank oil, it gives no dga evidence.  (The bushing oil is separate from the main tank oil)  If it is associated with externally visible connection of hv bushing, it might show on infrared (we don't know if that's the case).  If it's associated with the bushing internal insulation degradation/contamination, then likely wouldn't show up on anything other than power factor testing of the bushings, but the time-frame for that testing is limited to outages.

=====================================
(2B)+(2B)'  ?

RE: Indian Point SD

Electricpete,

I fully agree. Question for you since you seem more familiar with nuc plants than myself. I know on a decent amount of civilian plants, on HV transformers, they have installed automated DGA units that sample periodically over a set period.

I'm curious to see when the last Doble test on the bushings (C1, C2 tests) were done.  

RE: Indian Point SD

(OP)
OK, I worded that poorly. I was refering to vpl's comment regarding the level of maintenence decreasing because no one wants to pay for it. Of course a full battery of tesing should be done, but if you only do one thing and have a very small budget for PM's, I would do a DGA.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Solutions Brief - Protecting and Rescuing On-Ground Personnel
Keeping our warfighters safe and delivering them a competitive advantage is a key goal of departments of defense around the world. It’s a goal shared by embedded computing manufacturers like Abaco: we never forget who we serve.This case study describes how a major international contractor integrated an Abaco single board computer at the heart of its CAS/CSAR solution. Download Now
Datasheet - Top Enhancements Creo 7.0
PTC's Creo 7.0 has breakthrough innovations in the areas of generative design, real-time simulation, multibody design, additive manufacturing, and more! With Creo 7.0, you will be able to design the most innovative products faster than ever before, keeping you on the cutting edge of product design and ahead of your competition. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close