Requirement for NFPA 25 and log books on site.

Requirement for NFPA 25 and log books on site.

Requirement for NFPA 25 and log books on site.

(OP)
There does not appear to be a requirement for the building owner to maintain a copy of NFPA 25 or a log book on site in the 2008 edition. I see where records are to be maintained and made available to the AHJ. Even as I look back to the 2002 and 1998 edition I don't see this requirement, yet somehow I notice that this has been carried forward over the years from somewhere. See attached AFSA cover page, items 5 and 6  for example.

Regards
Dave
Replies continue below

Recommended for you

RE: Requirement for NFPA 25 and log books on site.

(OP)
I just received a call from NFPA and they state the obvious; that it would be somewhat of a conflict of interests to write the code and then determine that the code SHALL be maintained on site. This begs the question though - why did AFSA have it in their inspection reports where a "NO" is presumably a deficiency?

Regards
Dave

RE: Requirement for NFPA 25 and log books on site.

That is a great question lightecho.
I have being complaining about this for years because NFPA 25 does not require for a copy of the standard to be on site however NFPA 13 says that upon completion of the job a copy of NFPA 25 must be provided to the building owner.
In my opinion AFSA reports are the worst in the industry for multiple reasons.
Stick to NFSA reports and your inspectors will do much better in their inspections.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close