Automatic Sprinkler requirements for Walk-in-Cooler
2

Automatic Sprinkler requirements for Walk-in-Cooler

Automatic Sprinkler requirements for Walk-in-Cooler

(OP)
Can anyone verify if automatic sprinkler heaeds are required in a 8'x10' portable walk in cooler?
Replies continue below

Recommended for you

RE: Automatic Sprinkler requirements for Walk-in-Cooler

Absolutely required.

From NFPA #13 2002 Edition

4.1 Level of Protection.
A building, where protected by an automatic sprinkler system installation, shall be provided with sprinklers in all areas except where specific sections of this standard permit the omission of sprinklers.

8.1* Basic Requirements.
8.1.1*  The requirements for spacing, location, and position of sprinklers shall be based on the following principles:
(1) Sprinklers shall be installed throughout the premises.
(2) Sprinklers shall be located so as not to exceed maximum protection area per sprinkler.
(3) Sprinklers shall be positioned and located so as to provide satisfactory performance with respect to activation time and distribution.
(4) Sprinklers shall be permitted to be omitted from areas specifically allowed by this standard.
==========

Looking through where sprinklers can be omitted, such as skylights, double joisted and tight construction or space filled with insulation, there is nothing about not having sprinklers in walk in coolers and freezers.

Additionally, from the NFPA website http://www.nfpa.org/faq.asp?categoryID=947#23312

Do walk-in type freezers, coolers, vaults and safes require sprinklers?      
        
Yes. As explained by Formal Interpretation 78-6, these areas require sprinklers because they are part of the premises. NFPA 13 requires that sprinklers be installed throughout the premises in accordance with Section 4-1.1. There are no exceptions provided which allow for sprinkler omission in these areas.


as far as the freezer being portable I find it hard to understand how a freezer of this size could be deemed portable other than just saying it is.

RE: Automatic Sprinkler requirements for Walk-in-Cooler

(OP)
What I mean by portable, it can be disassembled and moved to another location with relative ease. Nothing is holding it in the location. Sort of "plug and play".

RE: Automatic Sprinkler requirements for Walk-in-Cooler

As long as it is connected to the building it has to have protection, my advise would be a dry horizontal sidewall extending from the heated space into the cooler.  Be aware that some cooler/freezers have a reverse function, that is the fans emit hot air for thawing/deicing, check this as you might need a high temp. sprinkler.

spkreng, CET

RE: Automatic Sprinkler requirements for Walk-in-Cooler

JRS863,

Just because it is easy to move doesn't reduce the requirements for sprinkler protection.
 

RE: Automatic Sprinkler requirements for Walk-in-Cooler

(OP)
Understood. Thanks for your response.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close