Existing one way slab and beam floor system. New equipment leg is to be located near center of slab instead of on an existing beam and the slab can not handle the point load. Has anyone ever installed a new concrete beam between existing concrete beams in order to support the equipment leg or column from above.
Other options are to install a steel column up to the underside of the slab and locate under each equipment leg; slab would have to be checked as continuous beam.
cut opening in slab and install steel column through slab to support equipment above. This would be a frame with bracing below slab.
install steel or concrete transfer beam on top of slab to span between exisitng concrete beams. Would make beam stiffer than slab to avoid overloading slab.
Without providing all the details (equipment is a combustion turbine with a 32 kip load at each of it's six supports), any suggetions. Don't discuss dynamic loads, only trying to get as many viable options as possible for supporting the static loads.
Thanks for your help.
Other options are to install a steel column up to the underside of the slab and locate under each equipment leg; slab would have to be checked as continuous beam.
cut opening in slab and install steel column through slab to support equipment above. This would be a frame with bracing below slab.
install steel or concrete transfer beam on top of slab to span between exisitng concrete beams. Would make beam stiffer than slab to avoid overloading slab.
Without providing all the details (equipment is a combustion turbine with a 32 kip load at each of it's six supports), any suggetions. Don't discuss dynamic loads, only trying to get as many viable options as possible for supporting the static loads.
Thanks for your help.
RE: New concrete beam between existing concrete beams
This assumes you can design and construct an aedquate beam-to-beam connection using expansion anchors or adhesive anchors.
RE: New concrete beam between existing concrete beams
RE: New concrete beam between existing concrete beams
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
RE: New concrete beam between existing concrete beams
Pretty cheap and quick solution??
RE: New concrete beam between existing concrete beams
Dik
RE: New concrete beam between existing concrete beams
RE: New concrete beam between existing concrete beams
RE: New concrete beam between existing concrete beams
Michael.
Timing has a lot to do with the outcome of a rain dance.
RE: New concrete beam between existing concrete beams
If you add a stiffening element to the slab like that, and don't provide a load path directly into the supporting beam, I can visualize where you create a worse condition.
Think about this...the load is applied at a midspan of a slab with your bolted beam directly under it. Since the bolted beam is much stiffer than the slab, the load is directed into it and ...where? toward the beam ends where all the shear gets dumped back into the slab near the beam end. then the slab must take ALL the shear load from that point to the supporting beam...using a much smaller width of slab participating in the shear transfer.
If the beam isn't there, the load gets distributed outward, naturally, to a wider slab area where shear doesn't control.
So what do you think? does this make any sense?