ashare 90.1,2004 voltage drop calculation
2

ashare 90.1,2004 voltage drop calculation

ashare 90.1,2004 voltage drop calculation

(OP)
Hi Everyone,

I am working on a LEED® intenational project, that follows ASHRAE 90.1-2004 and we have some problems interpreting the concept of feeder conductors and its voltage drop (VD). I would be very thankful if anyone could help me with the interpretation, hope it is not too simple for this kind of forum. It might be easier if I ask it through an example:
I have a main feeder conductor (FC1)that ends in an "over current protection device"(OCDP). From that OCDP three feeder conductors start (FC2, FC3, FC4).
ASHRAE 90.1 states "Feeder conductors shall be sized for a maximum voltage drop of 2% at design load".
The question is if the voltage drop should be calculated through CASE 1 or CASE2:
CASE 1: VDFC1 + VDFC2 < 2%
        VDFC1 + VDFC3 < 2%
        VDFC1 + VDFC4 < 2%

CASE 2: VDFC1 < 2%
        VDFC2 < 2%
        VDFC3 < 2%
        VDFC4 < 2%
(I have attached a diagram of the question that might be helpful)
Thank you very much in advance!!!!

 
Replies continue below

Recommended for you

RE: ashare 90.1,2004 voltage drop calculation

Feeders require no more than 2%, branch circuits have an allowable 3%. The 90.1 User's Manual copies the NEC 2002 example exactly.

RE: ashare 90.1,2004 voltage drop calculation

Maurice is right, and as for your calculation, Case 1 is correct.

You're allowed 2% from service to the branch circuit origin, then 3% for the branch circuit.

That distance from the service to the branch circuit panelboard may actually be composed of several feeders, one from main entrance equipment to sub-distribution panelboard, then from sub-distribution panelboard to load center.  2% end to end.

Good on ya,

Goober Dave

RE: ashare 90.1,2004 voltage drop calculation

(OP)
Thank you very much both of you!!!! now is completely clear for me. Adapt to a foreign code is not always easy

Best!
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close