ashare 90.1,2004 voltage drop calculation
ashare 90.1,2004 voltage drop calculation
(OP)
Hi Everyone,
I am working on a LEED® intenational project, that follows ASHRAE 90.1-2004 and we have some problems interpreting the concept of feeder conductors and its voltage drop (VD). I would be very thankful if anyone could help me with the interpretation, hope it is not too simple for this kind of forum. It might be easier if I ask it through an example:
I have a main feeder conductor (FC1)that ends in an "over current protection device"(OCDP). From that OCDP three feeder conductors start (FC2, FC3, FC4).
ASHRAE 90.1 states "Feeder conductors shall be sized for a maximum voltage drop of 2% at design load".
The question is if the voltage drop should be calculated through CASE 1 or CASE2:
CASE 1: VDFC1 + VDFC2 < 2%
VDFC1 + VDFC3 < 2%
VDFC1 + VDFC4 < 2%
CASE 2: VDFC1 < 2%
VDFC2 < 2%
VDFC3 < 2%
VDFC4 < 2%
(I have attached a diagram of the question that might be helpful)
Thank you very much in advance!!!!
I am working on a LEED® intenational project, that follows ASHRAE 90.1-2004 and we have some problems interpreting the concept of feeder conductors and its voltage drop (VD). I would be very thankful if anyone could help me with the interpretation, hope it is not too simple for this kind of forum. It might be easier if I ask it through an example:
I have a main feeder conductor (FC1)that ends in an "over current protection device"(OCDP). From that OCDP three feeder conductors start (FC2, FC3, FC4).
ASHRAE 90.1 states "Feeder conductors shall be sized for a maximum voltage drop of 2% at design load".
The question is if the voltage drop should be calculated through CASE 1 or CASE2:
CASE 1: VDFC1 + VDFC2 < 2%
VDFC1 + VDFC3 < 2%
VDFC1 + VDFC4 < 2%
CASE 2: VDFC1 < 2%
VDFC2 < 2%
VDFC3 < 2%
VDFC4 < 2%
(I have attached a diagram of the question that might be helpful)
Thank you very much in advance!!!!
RE: ashare 90.1,2004 voltage drop calculation
RE: ashare 90.1,2004 voltage drop calculation
You're allowed 2% from service to the branch circuit origin, then 3% for the branch circuit.
That distance from the service to the branch circuit panelboard may actually be composed of several feeders, one from main entrance equipment to sub-distribution panelboard, then from sub-distribution panelboard to load center. 2% end to end.
Good on ya,
Goober Dave
RE: ashare 90.1,2004 voltage drop calculation