I have an 8" globe valve mounted horizontally on a 300psi hydraulic line. Even after overhauling the valve, it still passes. Could the horizontal orientation of the valve be part of the problem? Are some valves better than others in certain orientations?
Thanks!
Thanks!





RE: valve orientations
The characteristic of globe valve (particularly metal to metal seat and closure) is to leak
Regards,
Truth: Even the hardest of the problems will have atleast one simple solution. Mine may not be one.
RE: valve orientations
Also how is the disc (plug) guided? If it is the body, is there full (or nearly full contact) or are there guide ribs? If not body, then how?
RE: valve orientations
Position of the valve is not so important in the case of globe valve.In this perticular case the seat(metal to metal contact)may be worn-out or the stem centre line is not exactly perpendicular to the seat plane and hence a small gap exits around the circumference when the valve stem is tightened .I pressume this may be one of the reasons for the leak.
RE: valve orientations
RE: valve orientations
Best regards,
Lakeshore Tech
RE: valve orientations
RE: valve orientations
since the valve has been "overhauled" (presuming that means either new seats installed or the old one cleaned inspected and reinstalled in good condition) that the valve has metal seats and they are either ANSI CLass III or Class VI which allows for leak by.
Check the valves specifications and if the seats are metal, then if you want a positive shuttoff (bubble tight) then you will need to change to a soft seated material.
Keeping in mind that the ANSI Standard for Class VI or bubble tight only applies to the test conditions (Air or Nitrogen @ 50 - 125 F 50 psig or Maximum operating differential pressure whichever is less). So if you hydrallic fluid at 300 psi there can be leak by and the valve will stilll meet the standard.
Check with the manufaturer and see what they can do for you to achieve the desired results you need.
RE: valve orientations
RE: valve orientations
If it is the former, what is the design rating of the valve? Almost all big sized globe valves(DN125 & above)can only withstand a certain limit of differential pressure across the valve.Once the limit is crossed, most manufacturers would recommend the use of a balancing disc which is designed to reduce this d.p. so that the valve can be easily open/close.
If the valve is of the former(pneumatic/electric actuated), then, would recommend that you check the closing force of the actuator and as they were mentioned, to which class is the leakage rate of the valve is being designed for.
Hope this is helpful.
Best regards,
Alex
RE: valve orientations
please guide us.
RE: valve orientations
Thanks again.
Christine.