MEASURING 1inWC WITH SENSOR SWITCH

MEASURING 1inWC WITH SENSOR SWITCH

MEASURING 1inWC WITH SENSOR SWITCH

(OP)
HI,

I am working on an application where Type X pressurization/purge is requiered to an enclosure where a AB 2711P HMI is installed. The custumer requieres to use 10-12 inWC pressure and then we set to measure this pressure with a presso-swtich AirLogic 4100-50. Happen that this HMI model, become leaky on the bezzel, so I asked AB and they told me that 0.5inWC is the maximum allowed pressure. Now, I can lower and control this pressure, but, I could not find so far, a sensor or switch being able to detect this set point. Can somebody enlight this dark scenario?

Regards,

  
Replies continue below

Recommended for you

RE: MEASURING 1inWC WITH SENSOR SWITCH

The domestic US requirement for type X, Y and Z purges and control rooms etc. per NFPA 496 is positive internal pressure of at least 25 Pa (0.1 in. of water) above the surrounding atmosphere.  10-12 inches would be two orders of magnitude greater than required by NFPA 496 for atmospheric applications.  The atmosphere within the enclosure must also be below the ignitible concentration of the combustible material.

RE: MEASURING 1inWC WITH SENSOR SWITCH

(OP)
Agree 10-12in is way too much and based on customers original pressure (we are cloning their system). We are now reducing as much as possible, but still need sensors for that. Most of the 9 enclosures can use 5in. HMI's enclosures should use no more than 1in. I will ask the purge enclosure manufactures for their sensors.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close