×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Earth Leakage Faults

Earth Leakage Faults

Earth Leakage Faults

(OP)
I have been given the enviable? task of tracing several earth leakage faults in several medium to large shops, basically the bulk of the fault current (measured in the switchroom on an ammeter which I cannot confirm as to the accuracy. It is over 30 years old) is on the lighting circuits, the bulk of which are fluorescents with starters and ballasts although these are not that old probably 8-12 years. This is confirmed by literally turning off two of  the fuseboards and the fault drops by about 5 amps.

We have carried out a random sample earth leakage test using a PAT tester and gained readings of approx 0.1 to 0.2 milliamps over 3 ballasts,however this does not allow for the control gear cooling down after isolation before testing, we have also "meggered" the fuseboard with the lowest reading being 4 megohms which although low is acceptable and this one circuit has no more of an impact than any of the others.

As you are aware this type of equipment gets extremely warm and I feel this is causing a breakdown in the insulation inside the gear, I have been told that we as a firm need to prove this to the client probably to allow the responsibilty to be passed to the lighting maintenance contractors.

I have found the info on this subject to be a little sparse?
and wonder if anyone has experience in this field and may have some useful insights as to the possible cause, also it only appears to be on older equipment, and do harmonics play a part in increasing the readings obtained at the sitchroom meter.

Thanks

RE: Earth Leakage Faults

It is worth speaking to the light fitting manufacturer to get their opinion, or contact the IEE who I am sure would be very helpful.

RE: Earth Leakage Faults

Conventional magnetic ballasts will produce a fair amount of third harmonics.  These will sum at the neutral point of a wye-connected system, and may appear as "ground" current, depending on how your ammeter is connected.  A standard ammeter will probably respond in some fashion to third harmonics.  

These are not really ground currents, since they will return in the neutral conductor to the transformer.  But if your neutral conductor has become open-circuited for some reason, these third-harmonic currents may be able to find an earth path back to the transformer neutral, depending on your grounding.  

RE: Earth Leakage Faults

Scragger,
I investigated a similar problem. In the fluorescents both fixed wiring and the internal wiring of the fluorescent itself passed close to the ballasts and were literally squeezed between the ballast and the wall of the fluorescent enclosure. In use the ballasts warmed up and caused low insulation resistance values between live conductors and earth ( measured with a low range clamp meter). These low readings were, like yours, not apparent when the circuits were tested with the supply disconnected.
I never PAT tested individual units but protective conductor currents of 0.1ma from 1 fluorescent, would seem rather unacceptable.

Regards,

Lyledunn

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - PLM and ERP: Their Respective Roles in Modern Manufacturing
Leading manufacturers are aligning their people, processes, and tools from initial product ideation through to field service. They do so by providing access to product and enterprise data in the context of each person’s domain expertise. However, it can be complicated and costly to unite engineering with the factory and supply chain. Download Now
White Paper - Medical Device Design Control
Medical device product development is a highly integrated and regulated process. Implementation of a requirements tracking solution requires attention to a variety of nuanced topics. When presented with the task of tracking the many concept relationships in a project of this type, the initial software solution of choice tends to be a two-dimensional text systems. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close