Hi,
I'm doing a coordination study for an underground distribution system.
There are padmount transformer, 500 kVA, 25kv/120-208V protected by two fuse in serie
1-Expulsion fuse link ABB 1B11144G10 (25 A)
2-Current limiting fuse Cooper 3544100M71M (100 A)
Upsteam of that, there is a switching device protected by 1 fuse:
1-Expulsion fuse link ABB 1B11143G12 (40 A)
There is a coordination problem between the switching device and the transformer protection. A solution is to change the 25 A fuse of the transformer by a 15 A. But i'm not sure if i change the expultion fuse, should i change the current limiting fuse for a lower rating too? Can i change the CLF? There is nothing in the literature which talk about the interrupting capacity of the ABB fuses, and it say that it must be used in series with a current limiting fuse or isolation link.
Also, the 40 A in the switching device isn't used with current limiting fuse. There's only a breaker upstream with the instantaneous at 1320 A. Is this arrangement OK?
The short cicuit current at 25kV can be up to 12 kA. The Bay-O-Net fuse link from Cooper, which is an equivalent of the ABB fuse link have an interrupting capacity of 2500 A.
Thanks
I'm doing a coordination study for an underground distribution system.
There are padmount transformer, 500 kVA, 25kv/120-208V protected by two fuse in serie
1-Expulsion fuse link ABB 1B11144G10 (25 A)
2-Current limiting fuse Cooper 3544100M71M (100 A)
Upsteam of that, there is a switching device protected by 1 fuse:
1-Expulsion fuse link ABB 1B11143G12 (40 A)
There is a coordination problem between the switching device and the transformer protection. A solution is to change the 25 A fuse of the transformer by a 15 A. But i'm not sure if i change the expultion fuse, should i change the current limiting fuse for a lower rating too? Can i change the CLF? There is nothing in the literature which talk about the interrupting capacity of the ABB fuses, and it say that it must be used in series with a current limiting fuse or isolation link.
Also, the 40 A in the switching device isn't used with current limiting fuse. There's only a breaker upstream with the instantaneous at 1320 A. Is this arrangement OK?
The short cicuit current at 25kV can be up to 12 kA. The Bay-O-Net fuse link from Cooper, which is an equivalent of the ABB fuse link have an interrupting capacity of 2500 A.
Thanks