Profibus Problem at MCC

Profibus Problem at MCC

Profibus Problem at MCC

(OP)
Dear All,
We have connected our whole MCC panel with profibus including constant speed and variable speed motors. Today I have found that about 20 motors were giving communication problem. When these were reset they became ok. But this kind of problem frequently occurs with 2 or 3 motors giving communication problem

RE: Profibus Problem at MCC

The #1 cause of that is people making up their own Profibus cables, thinking it's no big deal. It is.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: Profibus Problem at MCC

Does the communication problems only happen when the VFD's run?
If yes, then it is probably a cabling issue as jraef indicates. VFD's, as well as varying the frequency, are a good method of finding poor installation techniques and inferior cables. The problem is not the VFD btw.
If comms problems are there all the time, it could be the type of connectors/cables used but could be something deeper.
 

RE: Profibus Problem at MCC

From the information you provide it could really be a number of problems.
The specifications for the physical layer of a Profibus network are very strict, and if any of the requirements is not followed it could lead to problems.

To start you may want to make sure all components (including cables and connectors) are Profibus certified.
If they are make sure the physical dimensions of your network are within spec. Not only the total bus length is specified, also the MINIMUM length between two slaves is specified. Next step is to make sure all your bus parameters are OK.
You can check IEC 61158, or contact the experts (like procentec - see djs' post above) for more information.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close