Control a pumping system off pressure or flow?
Control a pumping system off pressure or flow?
(OP)
Looking for opinions here... I'll try to explain this as best I can. I have a pumping system consisting of two identical 150 hp 3600 rpm pumps in parallel that provide water to a variable load. The pumps take common suction from a tank. Sometimes there is no demand throughout the day, sometimes both pumps are required to meet the demand. The service is well kill water and the pumpage is 150° F oilfield produced water.
Sometimes the load is below one of the pumps' rated minimum flow so there is a variable FCV bypass to bypass some of the discharge back to the tank. The system must remain pressure charged at all times so that there is adequate flow when the need arises. This is sort of like a firewater system, in that the system has to stay pressured up all the time in case there is a demand. The system is controlled by a local PLC. I am stuck with making these two big pumps work, else I would recommend one big pump and a smaller jockey pump.
I am in a debate with the owner's engineer as to whether this system is better/more easily controlled using a discharge pressure signal or a flow signal to stage the pumps off and on line. I claim the load is better met, and the controls will be more stable, i.e less stops and starts, controlling the pumps off flow; he claims pressure.
My plan is to set the pumps to come on-line each day at 5 am since there is no demand at night. If there is intially no demand upon startup, i.e. if the discharge FT says zero, then open the bypass valve and flow the minimum bypass rate for 5 minutes. If the discharge rate does not increase in this time, i.e. if there's no load, shut off the pump after the 5 minutes. The bypass valve and the second pump will be controlled off the discharge FT.
I'm thinking he may have a point in that it might be a good idea to stage the second pump on-line on a pressure signal. Opinions?
Sometimes the load is below one of the pumps' rated minimum flow so there is a variable FCV bypass to bypass some of the discharge back to the tank. The system must remain pressure charged at all times so that there is adequate flow when the need arises. This is sort of like a firewater system, in that the system has to stay pressured up all the time in case there is a demand. The system is controlled by a local PLC. I am stuck with making these two big pumps work, else I would recommend one big pump and a smaller jockey pump.
I am in a debate with the owner's engineer as to whether this system is better/more easily controlled using a discharge pressure signal or a flow signal to stage the pumps off and on line. I claim the load is better met, and the controls will be more stable, i.e less stops and starts, controlling the pumps off flow; he claims pressure.
My plan is to set the pumps to come on-line each day at 5 am since there is no demand at night. If there is intially no demand upon startup, i.e. if the discharge FT says zero, then open the bypass valve and flow the minimum bypass rate for 5 minutes. If the discharge rate does not increase in this time, i.e. if there's no load, shut off the pump after the 5 minutes. The bypass valve and the second pump will be controlled off the discharge FT.
I'm thinking he may have a point in that it might be a good idea to stage the second pump on-line on a pressure signal. Opinions?
Thanks!
Pete
pjchandl@prou.com
RE: Control a pumping system off pressure or flow?
1) Controlling the flow (by pass flow)
2) To determine when to turn the 2. pump on
I can only come up with something for 2. (for now):
I beleive that using P for turning the 2. pump on will be the most reliable thing. But you have to think about when to turn it off not to get a situation where the pumps turn on anf off constantly.
Best Reagards
Morten
RE: Control a pumping system off pressure or flow?
A pressure switch after the end user pointin the header can be better option. Try to control the flow with a variable speed drive. This will give you better result.
Regards,
RE: Control a pumping system off pressure or flow?
Quark is right. Use a pressure control sensor (not switch) to maintain a constant pressure in the system. Write a program into the PLC that monitors the pressure sensor. Then you speed up or slow down the motor (hopefully, you have a variable drive motor) to adjust the flow.
In essence, you will be doing both. You monitor the pressure and adjust the flow to maintain a constant pressure.
There is an alternative also. There is a valve made by "Cycle Stop Valves" that will vary the flow without variable speed. There literature says they are at www.cyclestopvalves.com this valve is definately worth looking at.
Stressriser
RE: Control a pumping system off pressure or flow?
Unfortunately I do not have variable-speed drives avaialable for this, and I'm not sure the project will justify the use of VFDs, although I still have to run through the economics. I should have mentioned that in my first post.
Thanks!
Pete
pjchandl@prou.com
RE: Control a pumping system off pressure or flow?
RE: Control a pumping system off pressure or flow?
What do you think about TWO pressure switches, one for each pump. One pump, call it base pump, will have setting eqivalent to pressure that fully opens bypass so it will run as long as you have any flow demand.
The other (peak pump) will have setting bellow fully closed bypas setting.
Of course, you can alter the pumps every week to have same working hours.
RE: Control a pumping system off pressure or flow?
High-high pressure -- only one pump running, open FCV bypass
High pressure -- one pump running, close bypass
Low pressure -- two pumps running
Of course, you would have to design deadbands around the pressure stages to keep the pumps from switching on and off all the time when close to one of the transition points. Are you planning on having at least one pump run continuously during the day?
RE: Control a pumping system off pressure or flow?
I assume that either the pumps are connected to a common manifold, souce the water from the same reservoir and use the same return diverter pipe.
This diverter pipe has some sort of porportional valve that can be controlled by an input signal.
The pumps are either on or off and the they maintain a constant output pressure/flow.
One can monitor both pressure and flow either before and after the diverter pipe.
The requirements are that upstream pressure is maintained at all times during operations so a pressure sensor is needed upstream to monitor and to control the proportional valve. A flow sensor after the proportional valve will determine the requirements of the system and enable starting of the second pump.
Depending on the starting charcteristics of the pumps you may need a pressure relieve circuit if the proportional valve is not able to react fast enough. However if you have soft start on the pumps and proper settings, you may not need it.
This type of system will also allow rotation of pump usage so that you don't have one pump working all the time while the other idles most of the time. This is important to the life of the pumps.
Hope this helps.
Antonio Reis
01 209-834-1900
www.vitrom.com
RE: Control a pumping system off pressure or flow?
Control the pressure, not flow. You can't control the system by flow - if you think about it for a minute, you'll see why. What would a sensed reduction in flow cause the pumps to do? Ramp up? So when the system is not demanding any water, the pumps will be at max capacity...
My sticking point & purpose of this post is a VFD. I think this is the perfect (and essential) application for it's use. -Chas