The IBC 06 (or in my case the 2007 CBC) refers to ACI 530 for masonry design. ACI 530 gives a formula for development of bars in tension (2.1.10.3) that seems to yield some extremely long development lengths. Has anyone else ran into this issue? Any thoughts?

 

RE: Masonry Development Length

Yeah, these relatively recent changes suck.  I assume it's a result of some new testing.  I hate having to argue these type of code changes with contractors.

RE: Masonry Development Length

Actually, I thought masonry had some rather short development lengths.  The last time I looked was ACI 530-05, but they seemed shorter than a comparable bar for concrete.
For a #4 bar centered in an 8" wall and f'm=2500 psi, the development length is only 15.6".  I think that is pretty short, not too long.

RE: Masonry Development Length

IBC 2006 section 2107.5 was in fact revised and shorter splice lenghts are now shown. Their is however a stipulation indicating 50% more length than required by the calculations depending on the stress in the splice.

RE: Masonry Development Length

Nice post Steve.

That TEK note is showing an Ld of 21" for a #4 bar in 1500 psi masonry., this also translates into the 15.6" Ld for 2500 psi masonry that I mentioned above.  The best case (shortest) Ld for a #4 bar in 4000 psi concrete is 19".
As I said earlier, the development lengths for masonry seem too short, not too long (when compared with a comparable concrete assemblage).

RE: Masonry Development Length

(OP)
Thanks Steve for the info.

I agree that for smaller diameter bars (i.e. #4 or #5) centered in a masonry wall have reasonable development lengths. However, we design a lot of retaining walls where we end up with larger bars (#6 or #8) located closer to the edge for moment capacity. This results in VERY long development lengths that are even longer than the required lap splice lengths. The equation seems to be very sensitive to the K value.

One thing a co-worker brought up was the use of fy in the equation. Why do we use fy (60 ksi) when ACI 530 puts a maximum limit on the allowable tensile stress at 24ksi. It seems like the development length equation should have an Fs term instead of fy. This is just a discussion we had recently. I could be missing something obvious.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources

eBook – How to Choose the Correct Corrosion Testing Method
When designing a metal component, engineers have to consider how susceptible certain alloys are to corrosion in the final product’s operating environment. In a recent study by NACE (National Association of Corrosion Engineers), it was estimated that the direct and indirect costs of corrosion in the United States is approximately 6.2% of the GDP. In 2016, that cost exceeded $1 trillion dollars for the first time. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close