Corridor Live Load Clarification
Corridor Live Load Clarification
(OP)
We are having discussion in our office about when to use 40psf for multi-family corridors and when to use 100psf and would like to know if anyone has ever gotten word from IBC for a clarification.
The code says that you can use 40 psf for private rooms and the corridors servicing them and 100 psf for public rooms and corridors servicing them. What constitutes a public room, Elevator lobby, storage closets, vending rooms...?
When we have apartment buildings with units only we are using 40 psf for the corridors. It is being argued that when they add an elevator now there is public space so we have to switch to 100psf. Any thoughts?
The code says that you can use 40 psf for private rooms and the corridors servicing them and 100 psf for public rooms and corridors servicing them. What constitutes a public room, Elevator lobby, storage closets, vending rooms...?
When we have apartment buildings with units only we are using 40 psf for the corridors. It is being argued that when they add an elevator now there is public space so we have to switch to 100psf. Any thoughts?
RE: Corridor Live Load Clarification
Storage closets - no as they are ususally locked. However, if these can be heavily loaded, they may require a storage load. If they are only janitor closets, then 40 psf.
Vending rooms - yes
Anthing that is accessible to the public, as a hallway to individual apartments, is 100 psf, but not the hallways within those same apartments - those are 40 psf.
Mike McCann
MMC Engineering
RE: Corridor Live Load Clarification
RE: Corridor Live Load Clarification
Mike McCann
MMC Engineering
RE: Corridor Live Load Clarification
Don Phillips
http://worthingtonengineering.com