If a beam is designed with a dynamic impact factor of "2," what would the equivalent drop height?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Contact USThanks. We have received your request and will respond promptly. Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting Guidelines |
|
Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.
Here's Why Members Love Eng-Tips Forums:
Register now while it's still free!
Already a member? Close this window and log in.
RE: Dynamic load
Assuming that when you refer to an impact factor of 2 you mean that you have multiplied your static stresses and deflections by 2 to allow for dynamic effects, then you may be surprised by the answer.
You will double your 'static' stresses etc by simply applying the full load 'suddenly', and you don't need to drop it at all.
For most purposes, we calculate the deflections etc on the basis that the applied load is increasing proportionally to the deflection. That gives us a linear (triangular) graph for load/deflection. Since the area under the graph gives us the strain energy, the final strain energy = 0.5*W1*delection, where W2 is the final load.
If a load W2 is applied at full value from the very beginning, the load/deflection graph is a horizontal line, and the area underneath is a simple rectangle, thus the strain energy is 1.0*W2*deflection.
Thus for the same strain energy, stresses and deflections, W2=W1/2.
If you were to apply the original load W1 suddenly, you would end up with 2*deflection etc.
Thus any drop at all will generate an impact factor greater than 2