Safety in Distributed IO - EUROPE

Safety in Distributed IO - EUROPE

Safety in Distributed IO - EUROPE

(OP)
Hello,

I am trying to put together a main panel using Siemens an S7-300 with a ET200S. I have a Main Panel (contains the S7-300) and 2 more Aux. Panel that contain the ET200S.

I have already looked over the safety regulations for Europe and the class for the installation is the lowest. (I am using a safety relay).

This safety relay cuts the control power to the ET200S.

Is this correct? Or do i need to install several contctors in order to cut the power to thoses Aux. Panels? If so can i put the contactors on the Aux. Panel?

Thank you in advance.
Replies continue below

Recommended for you

RE: Safety in Distributed IO - EUROPE

mastayoda,
Use the fork Luke.

It has been my experience that it is best to drop the control power relay with the safety circuit. If the safety relay drops (e-stop button pressed or a guard switch actuated) a contact wired in series with the control power relay coil should do it.
Your discrete i/o nodes should be powered through a contact on your CRM or an aux. contact on the safety relay.   
Another method is to drop discrete output power through the crm connected to motion outputs supply only.

Good luck


 

RE: Safety in Distributed IO - EUROPE

(OP)
Thank you Professor for your reply.
(gratefull i am)

At this point i have more or less what you have said. And i usually do like you have said.

My safety relay connects/disconnects the comand power from the main panel and 2 more control power relays on the auxilary panels (the power supplys were from client and i have no way of changing it).

But i still do not know whether this complies to European specifications.

I have read several papers on the subject and even the ISO rules and everything seems to point to contactors that cut the power (not the control) from all the equipment.

Cheers.

RE: Safety in Distributed IO - EUROPE

(OP)
Pardon my ignorance Prof. but what do you mean with CRM?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close