Real RS-232 Cable Length Limit
Real RS-232 Cable Length Limit
(OP)
175 cable feet of STP between a PC comm port and the DCE--think it'll work at 9600, at 19.2k? I'm not looking for what the specs say but what your experiences are. Cut sheet for the cable says 40pF/ft @ 1.0 MHz.
Dan B
Dan B
RE: Real RS-232 Cable Length Limit
Oh..
40pF/foot... That sucks.
Maybe not. If it doesn't, it's your crummy cable.
It's a hard call really as it also depends on your electrical environment. I would imagine 9600 would be dependable. Maybe 19.2k with good cable. In a benign place.
Hopefully you are driving the cable with nice levels not some laptop with +/- 3V levels.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Real RS-232 Cable Length Limit
If it's a dollar a foot plus connectors and labor, $200?
What about a couple 232/485 converters, one for each end, and 200' of twisted pair that you've already got lying around, instead? Far higher probability of it working.
Dan
RE: Real RS-232 Cable Length Limit
Black Box EDDC
but on the - side it is expensive.
RE: Real RS-232 Cable Length Limit
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Real RS-232 Cable Length Limit
RE: Real RS-232 Cable Length Limit
Current loop should work okay.
Mike Halloran
Pembroke Pines, FL, USA
RE: Real RS-232 Cable Length Limit
http://ww
They don't say at what baud rate. Might be 300. But I think 175ft is possible. I had about 120 feet that we used all the time for various serial endeavors at speeds up to 34,5k and I don't remember having any problems.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Real RS-232 Cable Length Limit