On breakers there is a difference between what the main contacts can interrupt, once, and what the contacts can carry without interrupting. And it would be the same for bus bar in that it has a carry capacity.
The carry capacity is typically a I^2T function and the ability to disapate heat and remain below the melting tempenture.
The interrupting rating is the ability of the main contacts to handle the arc interrupting on the current for one operation. If the breaker is expected to interrupt a fault more than once between contact replacments it needs to have a greater interrupting rating to allow for the contact wear factor.
Also you will find there should be an additional rating called the capacitor switching rating, which is a measure of the contact speed and opening distance and the ability to operate with near 90 degree angular difference between the current and voltage.
Probally to much information, but I sometimes can't stop in mid stream.