existing steel/conrete building

existing steel/conrete building

existing steel/conrete building

(OP)
I am working on a project that has steel I-beams that are encased with concrete carrying a concrete floor. From the underside of the floor there are 1'-0"x1'-0" terracotta tiles within the concrete slab. It looks like these were placed in the concrete form and the slab poured around them. In between these tiles there are areas of exposed rebar. This building is very old, does anyone know anything about this type of framing or know of any good reference material on it.

Anyone know of a good method to repair the exposed rebar?
Replies continue below

Recommended for you

RE: existing steel/conrete building

It is called a pot and beam or a clay pot slab in the uk.

Basically works similar to modern ribbed forms but the clay pots act like void formers.

RE: existing steel/conrete building

I worked on one recently.

The Riddick Laboratory/engineering bldg building at NC State Campus in Raleigh North Carolina had both the terra-cota forming and the concrete encased steel structure.  i couldn't find any information on it with a search, but i'm sure there must be something since it was very much in their own backyard. the renovation started 3 years ago and was a full gutting structural/architectural renovation of the building.

RE: existing steel/conrete building

Check out page 266-268 of 1923 Carnegie Pocket Companion on sliderule's website (under misc. publications and documents).  Is that what you have?

http://www.slideruleera.net/

RE: existing steel/conrete building

(OP)
No, neither of those articles is what I have. Mine structure is not arched.

RE: existing steel/conrete building

It sounds like a typical "floor filler" slab system that is/was used in Europe. The hollow clay tile (or concrete block, concrete/wood fiber, AAC, etc.) are used to decrease the weight and provide a flat ceiling for finishing. They are still used in many reisdential projects and there are EU standards for the materials for the fillers. Usually these are just one way systems, but you seem to be describing a two way system.

I am not an expert on the repairs, but the cleaning and developing the strength of the rebars will be a big challenge.

RE: existing steel/conrete building

deereman,
those references don't match what i saw either at the NC State Civil Egr school.

RE: existing steel/conrete building

The Carnegie handbook has flat terra cotta arches. They don't look like arches.

RE: existing steel/conrete building

Actually the article from Structure Magazine from my earlier post also has flat clay tiles in Figures 2 and 3.

RE: existing steel/conrete building

deereman,

It is a pretty simple concept. The clay tiles dont do much apart from holding up the concrete between the beams.

The concrete between the tiles act as simple T beams and should be analysed as such.

Beware that the shear capacity is very low for these slabs.

RE: existing steel/conrete building

Hello deerman,

From all the above responses and your description of the floor, I would suppose you are referring to a ribbed slab or a waffle (2-way ribbed slab). If so, csd72 already told you the regular design considerations just as a T-beam. the shear at the ends need to be checked and usually the ends require some thickening to take care of some rotation and moments.

As per the repairs, ithe method to use will depend on the necessity of repair after you have carried out your inspection and investigations. Corrosion resulting from  cover inadequacy is a major consideration for durability and strength but you may be able to addd new rebars to substitute for these effect.

Consideration of use of stirrups, or rings are optional but usually depend on the shear capacity of the concrete.

Shotcrete concrete is best used in repairs.
Let us have a few of your concerns and we can give our comments.

Thanks

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close