stormwater pipe sizing

stormwater pipe sizing

stormwater pipe sizing

(OP)
I have a 5 acre watershed, 7 minute time of concentration, 8.5 inch per hour storm intensity, and .5% slope for my pipe.  The flow out of the watershed into the pipe indicates that I need a 36 inch diameter pipe.  

I feel I have followed standard design procedures but a rainfall of 8.5 inches per hour just seems like a lot of rain for my 5 acre watershed.  

Just want an opinion-would most people go with the 8.5 inches per hour storm intensity and have a 36 inch pipe or would you back that number down to something smaller to get away with a smaller pipe because 8.5 inches is a lot of rain.  

just so you know
I am probably going to use the 8.5 inch per hour intensity because it is standard design procedure.

RE: stormwater pipe sizing

8.5 inches per hour is a rainfall rate that is unaffected by the size of the site.  It sounds like a 100-year storm intensity. Around here a 7-min duration/100-year storm would suggest an intensity of 8 in/hr whereas a 10-year storm would suggest 6.2 in/hr and a 25-year storm would suggest 6.8 in/hr. As you can tell, there's not that much in it.

Fudging your rainfall numbers probably won't help you much, certainly not as much as increasing the slope on your pipe and putting on a good headwall would. Of course, detaining your peak flow would decrease your pipe size quite nicely.

RE: stormwater pipe sizing

.

francesca wrote: "8.5 inches per hour is a rainfall rate that is unaffected by the size of the site"

That may be the case for small watersheds, but - as pointed in various publications - pecipitation intensity decreases as watershed size increases.

See, for example; "Rainfall Input for Hydrologic Models" by David M Hershfield (http://www.cig.ensmp.fr/~iahs/redbooks/a078/iahs_078_0177.pdf).

Check out the Depth-Area curves and discussion.

.

tsgrue: site engineering, stormwater
management, landscape design, ecosystem
rehabilitation, mathematical simulation
http://hhwq.blogspot.com

RE: stormwater pipe sizing

.

Here's a graph of such...



.

tsgrue: site engineering, stormwater
management, landscape design, ecosystem
rehabilitation, mathematical simulation
http://hhwq.blogspot.com

RE: stormwater pipe sizing

"The site" is 5 acres, and francesca is correct that the rainfall intensity is independent of a site that small.  

Any idea what design storm your 8.5 inches/hour is?  You can't just change the rainfall intensity without either increasing your time of concentration or selecting a shorter-recurrence interval storm (say 10-yr instead of 100-yr).

RE: stormwater pipe sizing

You wrote:

"I am probably going to use the 8.5 inch per hour intensity because it is standard design procedure."

First, there is no universal "standard procedure". You may be required to design for some reviewing agency's "standard" but that doesn't mean that that is some universal standard.  It doesn't even mean that it is good practice.

Second, for this small site, the Rational Method may be OK but that also doesn't mean it is good practice or the best method to use.  There may be better data available.  Have you looked for it ?

Third, get a copy of the reviewing agency's standards and then ask yourself if you feel you need to be more conservative in your design. What are the consequences of failure of your design ? Can there be downstream damage, lawsuits or other problems ? What are the laws in your area ?
What are the physical constraints of the site ?  What does the storm water Master Plan ( if there is one ) call for ?

Does on-site detention make sense in this case or might it be required ?

good luck

RE: stormwater pipe sizing

I would start with checking your time of concentration.  7 minutes seems low, especially for a 5 acre site.  And many agencies limit the minimum Tc to 10 minutes.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close