Question about protecting plc contacts and other sensitive components from inductive loads. Specifically solenoids that actuate air cylinders (24vdc), electric clutch coils (24vdc and 110vac, and contactor coils(24vdc).
When is it best to use a simple diode, and when is it best to use a resistor/capacitor snubber or suppressor? I've heard diode obviously for the DC stuff and snubber for the ac stuff. I understand a diode won't help me with the ac circuit, but I've seen both diodes and r/c snubbers on dc stuff.
I always use one or the other but not always sure which is best? Any insight would be greatly appreciated.
When is it best to use a simple diode, and when is it best to use a resistor/capacitor snubber or suppressor? I've heard diode obviously for the DC stuff and snubber for the ac stuff. I understand a diode won't help me with the ac circuit, but I've seen both diodes and r/c snubbers on dc stuff.
I always use one or the other but not always sure which is best? Any insight would be greatly appreciated.





RE: Reverse current protection diodes and r/c snubbers
You cannot use a diode in AC for that solution so you use snubbers, (cap/resistor).
Snubbers dissipate power so are less desirable but they work very well.
A suppressor works well and dissipates much less power, only when actually 'suppressing'. Often they have a shorter life as they are mechanical and wear out.
Did this answer your question?
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Reverse current protection diodes and r/c snubbers
htt
http://focus.ti.com/lit/an/slup100/slup100.pdf
http://www.industrologic.com/mechrela.htm
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...