Dust/Lint in Control Cabinet
Dust/Lint in Control Cabinet
(OP)
I was assigned to a plant for a short term to help with some specific problems. On of them is dust and lint entering into the control cabinets. It is a textile plant that creates massive amounts of lint. We are thinking that the only way to keep the lint out is by creating a positive pressure in the cabinet.
We are planning on installing a central, filtered fan to blow air through ductowork to all of the panels in the plant. We want to do centralized to prevent daily cleaning of filters on every cabinet to keep air moving.
In order to estimate how much air I need to move, I was going to install a filtered 100cfm 4.7 inch fan on a cabinet and see how that does in keeping lint out.
Does anyone have any experience with this type of problem and countermeasures?
Does anyone know what type of air turnover might be needed? - 100cfm / 200cfm / 300cfm for a 100 cf cabinet, etc
We are planning on installing a central, filtered fan to blow air through ductowork to all of the panels in the plant. We want to do centralized to prevent daily cleaning of filters on every cabinet to keep air moving.
In order to estimate how much air I need to move, I was going to install a filtered 100cfm 4.7 inch fan on a cabinet and see how that does in keeping lint out.
Does anyone have any experience with this type of problem and countermeasures?
Does anyone know what type of air turnover might be needed? - 100cfm / 200cfm / 300cfm for a 100 cf cabinet, etc





RE: Dust/Lint in Control Cabinet
Consult a HVAC expert for the blower specifications.
Since you are only doing this to prevent dust from getting in, you don't have to worry about "turnover". All you need is positive pressure.
If you do have to "Purge" then you need turnover, and stagnet air needs to be controlled with flow measurement.
Charlie
www.facsco.com
RE: Dust/Lint in Control Cabinet
Please don't take this wrong, but your management needs to be aware that this is not something to assign to someone with no experience in this.
RE: Dust/Lint in Control Cabinet
My follow up question is this.....
These machines are from a major manufacturer, who does this all day long. The plant only runs synthetic fiber (yes they will conduct some current, so shorting is an issue, but not combustion. Would this still require redoing all of the cabinets? I am a bit skeptical that the textile machinery company would have installed the wrong type of cabinet, if it is, in fact, required by law.
Thank you for your post, and I dont mean to sound skeptical, but if you are in fact correct, then I need to know how hard I have to push back.
RE: Dust/Lint in Control Cabinet
RE: Dust/Lint in Control Cabinet
As for sizing the blower, this is something you can do it you want to make the effort. There are tables for calculating pressure drops for various pipe sizes and lengths, number of elbows, etc. It would also be a good idea to install gate valves (or other) in each line so you can balance the system. You may also need to restrict the exhaust from the enclosures as well, which may get tricky depending on number of vents, size, conduits, etc. Keep in mind that depending on the enclosure size, you could easily create a hazard by over pressurizing. Get some DP gauges to install in each enclosure, I think Dwyer Magnehelics are only about $60-$70.
Good luck.