Process Signal Wire Sizing

Process Signal Wire Sizing

Process Signal Wire Sizing

(OP)
Can anyone suggest a recognized standard (ISA, IEEE,...) that provides information on sizing 4-20mA process control wire? I am specifically looking for a recommended maximum voltage drop for the wire using a 24VDC, two conductor circuit.

Regards,
GaDawg

RE: Process Signal Wire Sizing

There are safety specs for industrial control wiring that call for 18 gage wire minimum.

RE: Process Signal Wire Sizing

This is an old thread but I can't stand not adding my two cents anyway.

I can't imagine that there would be a standard for such. The sizing for signal purposes would be dependent on how much voltage you have with your power supply after all the other load drops are considered. Then what you had left to work with would let you figure how many feet of what size you could use. Knowing the length, the size limitation would follow. 20mA doesn't drop much voltage unless the length is really long. I've never needed to even consider it unless out in a wastewater treatment situation where the signal goes thousands of feet.

But.... A practical consideration that will more likely govern the minimum length is how strong the wire or cable is when pulling through conduit. The rated pull stength may be the determining consideration. We never pulled single conductors less than 16 AWG for that reason but I've gone to multiconductors in the past to give good pull strength with smaller conductors usually #18 or #20.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close