Hello,
I am working on a 24 VDC Burkert Solenoid Valve. When bench testing it with a regular switching 24 VDC power supply I was unable to get the solenoid to engage but when re-installing the valve into service the PLC can drive the solenoid with no problems.
I am wondering why a PLC can drive the solenoid but a power supply in my shop can't. Anyone have an idea?
Thanks,
Adam
I am working on a 24 VDC Burkert Solenoid Valve. When bench testing it with a regular switching 24 VDC power supply I was unable to get the solenoid to engage but when re-installing the valve into service the PLC can drive the solenoid with no problems.
I am wondering why a PLC can drive the solenoid but a power supply in my shop can't. Anyone have an idea?
Thanks,
Adam





RE: PLC 24 VDC output vs. Test bench 24 VDC output
Happened to me 35 years ago; a small 12A/24VDC linear actuator drew a peak of ~275A when first switched on ... from a battery. Our QC department had declared it DOA when their 15A supply wouldn't start it.
Mike Halloran
Pembroke Pines, FL, USA
RE: PLC 24 VDC output vs. Test bench 24 VDC output