Ridge Vents in a Steel Diaphragm Roof
Ridge Vents in a Steel Diaphragm Roof
(OP)
I am designing a rectangular CMU building (42'x60') with single span cold formed steel trusses with a 4 on 12 roof pitch. I am using 1.5 Type B roof deck spanning perpendicular to the trusses as a diaphragm attached with #12 screws. Metal roofing will be placed on top of the metal roof deck. The architect wants to put a continuous ridge vent at the ridge the entire length. I believe that this will interupt my diaphragm. Does anyone have any ideas on how to keep continuity in my diaphragm?
RE: Ridge Vents in a Steel Diaphragm Roof
DaveAtkins
RE: Ridge Vents in a Steel Diaphragm Roof
RE: Ridge Vents in a Steel Diaphragm Roof
This would greatly affect diaphragm shear stiffness and possibly affect the design in that the flexible/rigid classification for diaphragms depends on relative diaphragm flexibility. You also may have chord force issues as well.
But in most "small" building cases, it may not be all that critical as you suggest. Just thought I'd point out my thoughts here.
RE: Ridge Vents in a Steel Diaphragm Roof
But, if it acts as 2 separate diaphragms when load is perpendicular to the ridge it, seems that something should be done along the boudaries at each side of the ridge. I would install blocking between the metal stud trusses at each side. Check the chord forces if it actually were acting as 2 separate diaphragms with load perpendicular to the ridge and see what you get.
RE: Ridge Vents in a Steel Diaphragm Roof
Another way of handling it (I read in the APA "Introduction for Lateral Design" for wood diaphragms) is to block a portion of the vent and double the attachements in the blocked portion of the ridge. The ridge vent would not be continuous and the diaphragm would be treated as having holes in it. This sounds applicable to my situation. Another question arises, how do you "block" a CFS Truss with light gage steel to create a tie for a steel deck diaphragm? Are there CFSF blocking members?
I would like to ignore the vent as Dave Atkins says. He is probably correct with such a small building, but I just don't feel right about it. It is just the perfectionist in me.
RE: Ridge Vents in a Steel Diaphragm Roof
ht
You can run a continuous hat channel attached underneath with a couple of screws at each truss. Or somebody else here may have a better idea.
RE: Ridge Vents in a Steel Diaphragm Roof
RE: Ridge Vents in a Steel Diaphragm Roof
In the past I have also looked at a wood diaphragm with a ridge vent, with wind PERPENDICULAR to the vent. What happens is, near each end of the diaphragm, where the shear is largest, there is horizontal shear (parallel to the ridge vent) from the roof sheathing on each side of the vent. These equal and opposite shears must be resisted by weak axis bending of the top chords of the trusses.
DaveAtkins
RE: Ridge Vents in a Steel Diaphragm Roof
RE: Ridge Vents in a Steel Diaphragm Roof
I'd worry more about the wind load parallel to the slot. In theory, you've broken the diaphragm into two separate diaphragms. Each diaphragm will be unsupported on the slot edge. The only way this works is if the chords at the edge of the building (perpendicular to the slot) can make the diaphragm continuous, or if the building can resist the torsion that will result from only one side being braced (and both sides in the other direction).
RE: Ridge Vents in a Steel Diaphragm Roof
1. Block every other space between the trusses and double the connections as if there are holes in the diaphragm. The Arch might not like this. The ridge vent would not be continuous.
2. Provide continuous blocking at either side of a the vent. Then I would put continuous straps on top of the blocking to act as a chord. This would make the diaphragm two diaphragms.
When the wind is parallel to the ridge is a bit more difficult.
1. I can do as I would in item one when the wind is perpendicular to the roof but the ridge vent would not be continuous.
2. I can do what I would do in item two above. Then place light gage straps between the two sets of blocking on either side of the vent. This would make the two diaphragms in the perpendicular direction one diaphragm in the parallel direction.
3. I can run a ridge drag beam under the top chord peak and use light gage straps to drag the wind into the shear walls.
I am a little worried on how I will get the forces into the chords (cmu bond beams) when the wind is parallel to the ridge. The end trusses sit on top of the CMU wall. The peak on the truss is 7' tall. I am having a hard time visualizing this. I usually deal with flat roof diaphragms.
RE: Ridge Vents in a Steel Diaphragm Roof
RE: Ridge Vents in a Steel Diaphragm Roof
RE: Ridge Vents in a Steel Diaphragm Roof
RE: Ridge Vents in a Steel Diaphragm Roof
Just an idea....
RE: Ridge Vents in a Steel Diaphragm Roof
DaveAtkins
RE: Ridge Vents in a Steel Diaphragm Roof
RE: Ridge Vents in a Steel Diaphragm Roof
I hope this helps!
RE: Ridge Vents in a Steel Diaphragm Roof