RE: Periodic Inspection
In theory the number of inspections needed to satisfy the "periodic" requirement is the number of inspections that the SI has determined are needed to convince him/herself that the intent of contract drawings/documents is being met.
In actual practice the frequency of periodic inspections is determined by the number of special inspector employed by a testing firm and the firm's current workload. When the work load is heavy there are fewer "periodic" inspections because the SI is run from job to job. When the workload is slow the SI is camped out on one job.
Like on masonry jobs, periodic means the SI doesn't have to see every single CMU block placed in a wall, but he still has to inspect the entire wall. Similarly on periodic for reinforcing on concrete work, the SI doesn't have to see every single bar as it is placed, but he has to inspect all the bars once in place.
Also under reinforced concrete, "Inspection for maintenance of specified curing temperature and techniques." Obviously the SI does have to sit there during the entire curing period, but he still has to perform the inspection.
RE: Periodic Inspection
I am not familiar with Chapter 17 of the 2006 IBC. However, in the 03 and 06 versions, there is no provision that spells out a frequency for performing periodic special inspection.....to the best of my knowledge.
Check out these links
http:/
h
RE: Periodic Inspection
All to often the SI is left out of pre-con meetings and is denied access to the SER. Contractors still have far too much influence over the process.
RE: Periodic Inspection
But the IBC language and the guidelines provided for the IBC provided by CASE seem to place the burden of specifying frequency of inspection on the "Registered Design Professional". I still have not found any recommendations of what this frequency should be - even general guidelines. How would you determine the specified frequency of periodic inspection?
RE: Periodic Inspection
It takes what it takes. No more and no less.
RE: Periodic Inspection
RE: Periodic Inspection
Is there any place for the EOR to find guidance on specifying this?
RE: Periodic Inspection
Here's what I do. I sit down and think about what is important design-wise and how critical each construction feature is in regards to performance. I also consider what areas contractors typically get wrong. I establish hold points and inspect at those intervals. As a minimum, I would probably visit the site near the beginning of a job and near the end. I'd add visits inbetween based on hold points. On a recent project for two tall steel stacks I visited the job site every fortnight.
Joe Tank
RE: Periodic Inspection
In the body of Chapter 17 there are some specifics regarding certain types of construction (high strength bolts, for example, and for welds one is referenced to AWS D1.1).
In my opinion, the entire inspection chapter is the result of bringing the UBC folks into the IBC fold. They (the UBC'ers) probably have a stronger opinion of what needs to be inspected, how often, and why. I don't posess such a strong feeling about the need or effectiveness of these "inspections".
In the end it seems to me that it is up to the EOR to specify and the Building Official to approve of the inspection program. If a liberal engineer meets up with a liberal building official the result may be not-very-frequent inspections. When everybody takes a conservative approach the cost of the special inspections may exceed the structural engineer's fee (I witnessed this happen on the design of a new High School). Sometimes it seems backwards to me that we will beat the geotech down to $15,000 for his professional recommendations, but then turn around and pay the testing arm of his firm $75,000 for field QA.