Suspended slab supported on three sides
Suspended slab supported on three sides
(OP)
Hi,
Can anyone give me some assistance in designing a slab on three sides?
I have a 7'-0"x15'-0" balcony and the architect does not want to have a front edge beam. I can either design as a cantilevered slab however I would like to keep the slab thickness to 6". I was considering cantilevering two beams but I'm not sure this will make much of a difference because of the aspect ratio. Can anyone give some advice on designing slabs supported on three sides and if this would make any difference.
Suggestions are also welcome.
Regards,
Adrian
Can anyone give me some assistance in designing a slab on three sides?
I have a 7'-0"x15'-0" balcony and the architect does not want to have a front edge beam. I can either design as a cantilevered slab however I would like to keep the slab thickness to 6". I was considering cantilevering two beams but I'm not sure this will make much of a difference because of the aspect ratio. Can anyone give some advice on designing slabs supported on three sides and if this would make any difference.
Suggestions are also welcome.
Regards,
Adrian
RE: Suspended slab supported on three sides
RE: Suspended slab supported on three sides
I would just cantilever the slab for the 7'. That is not that long of a cantilever and you shouldn't have any trouble keeping the slab at 6" thick.
Doing a very rough check of 100 psf LL, I am getting somewhere in the neighborhood of a #5 @ 12".
RE: Suspended slab supported on three sides
Your assumption is right however, what about deflection? Isn't that an issue, esp. since aci recommends an minimum of L/10 for slab thickness in lieu of more detailed assessment.
Regards,
Adrian
RE: Suspended slab supported on three sides
Yes, you will have to do a quick deflection check (probably by hand). I just did it with #6 @ 12" and the tip is under L/360 for total load.
RE: Suspended slab supported on three sides
You could look at a tapered slab thickness; 7" at the building tapering to 5" at the tip results in better performance for the same concrete volume.
RE: Suspended slab supported on three sides
Clefcon
RE: Suspended slab supported on three sides
RE: Suspended slab supported on three sides
one way spanning slab is actually worse.
Henri2
I'm not sure what you mean exactly
RE: Suspended slab supported on three sides
How do you do a quick calculation for deflection of concrete? Is there some sort of rule of thumb. The procedure I know is pretty invloved and includes calculating effective moments of inertia which is based on the dead and live load stresses. How do you account for long term deflection.
Regards,
Adrian
RE: Suspended slab supported on three sides
You are correct. The procedure is in section 9.5.2.3 of ACI 318-05. The long term deflection multiplier in is 9.5.2.5. Calculating Ie is not overly time consuming.
apsix-
You can get upward deflection with live load on backspan only, depending on magnitude of LL and length of backspan; however, the greater concern (I believe) is downward deflection. In addition, a tapered slab will perform better for deflection, but 7" to 5" is still not complying with the L/10 rule and deflection will still have to be checked. With the tapered slab, it is a much more time consuming process.
RE: Suspended slab supported on three sides
RE: Suspended slab supported on three sides
Roarks is a good option, otherwise estimate the proportions by deflection compatability and then check deflection based on the proportional loads.
Make sure you include bars for the one way spanning slab as well since the slab will crack otherwise.
RE: Suspended slab supported on three sides
In what sense? 15 foot span for a 6" deep slab is not all that unusual.
RE: Suspended slab supported on three sides
I posed the question regarding the influence of the support provided along sides which are 7 feet long because I was concerned that the slab would not behave as a true 7 ft span cantilever under loading...and some bending would occur in 15ft span direction.
IMO, analyzing the slab as a plate supported on three sides with one edge free as proposed by jmiec should be given some serious consideration.
RE: Suspended slab supported on three sides
I understand that beyond a slab aspect ratio of about 2 it wouldn't be worth it, so I would design it as a cantilevered slab without end beams, and not rely on an empirical L/10 thickness limit. It will look better without those beams anyway.
RE: Suspended slab supported on three sides
Thanks for the clarification.
RE: Suspended slab supported on three sides
RE: Suspended slab supported on three sides
Yogi Anand, D.Eng, P.E.
Energy Efficient Building Network LLC
ANAND Enterprises LLC
http://www.energyefficientbuild.com
RE: Suspended slab supported on three sides
I'm sure deflection is all you are worried about...
RE: Suspended slab supported on three sides
RE: Suspended slab supported on three sides
Tomfh...you are right that I am mostly concerned with deflections however savings in reinforcing steel for strength is also a benefit. While I believe that adding cantilevered beams on the 7'0 edge will help, I can't help but think the influence will be localised (ie a couple feet from the beam)since the aspect ratio is higher than 2. Do you have any source which illustrates your comments or is it something that you modelled?
The code limits cantilever thicknesses to L/10 unless you do more calculations. I'm going to take MYerges recommendations do a more detailed analysis for deflection.
csd72/jmiec....where can I find Rourke's formulas....is there a book that you recommend or an online source?
RE: Suspended slab supported on three sides
RE: Suspended slab supported on three sides
http://censoft.net/default.asp
RE: Suspended slab supported on three sides
We had the same situation (and the same argument) a few years back. I modelled it.