Why must a motor be inverter duty for vari-speed applications?
Why must a motor be inverter duty for vari-speed applications?
(OP)
Is there a rule of thumb for just how low a motor
speed can be reduced before the motor itself stalls?
If you have a motor speed of 1775 RPM and you want to
slow it down - let's 50% what comes into play within
the motor? Does it pull more or less amps? Just what
takes place when the voltage is reduced? I suspect
overheating would take place because the fan is not
cooling the outer shell adequately? Can you still
maintain phase balance at lower speed ranges or does
it drift?
speed can be reduced before the motor itself stalls?
If you have a motor speed of 1775 RPM and you want to
slow it down - let's 50% what comes into play within
the motor? Does it pull more or less amps? Just what
takes place when the voltage is reduced? I suspect
overheating would take place because the fan is not
cooling the outer shell adequately? Can you still
maintain phase balance at lower speed ranges or does
it drift?
Wayne E. Lovison
service-parts@naglepumps.com
RE: Why must a motor be inverter duty for vari-speed applications?
Certain Annixter cable specifically for inverter fed motors uses 2kV insulation.
RE: Why must a motor be inverter duty for vari-speed applications?
RE: Why must a motor be inverter duty for vari-speed applications?
Amps is generally determined by the load power (at high loads) which will usually decrease as speed decreases.
RE: Why must a motor be inverter duty for vari-speed applications?
Many factors influence how low the motor speed can go. Ignoring motor heating, in theory a vector control drive with tach feedback could provide 100% rated torque at 0 speed.
RE: Why must a motor be inverter duty for vari-speed applications?
Either approach is valid. The key is to specify the speed range your motor will operate at under normal service conditions
RE: Why must a motor be inverter duty for vari-speed applications?
dpc
RE: Why must a motor be inverter duty for vari-speed applications?
RE: Why must a motor be inverter duty for vari-speed applications?
Controlling the speed by a variation of the voltage using an transformer or a AC-Controller:
very cheap and only suitable for small motors with fan or pump loads, special motors with high resistance rotors required, for this type of drive stalling is an issue !
Controlling the speed by variation of voltage and frequency (using an inverter):
more expensive, but suitable in the range from a few W to several MW, can be used for all typs of loads, standard motors can be used in some applications
I guess all the other answers refered to the second type of drive, but I'm not sure if Lovison is really talking about an inverter drive.
RE: Why must a motor be inverter duty for vari-speed applications?
Can you run a non-inverter motor with a VFD? Some say
yes other's say you should buy a motor built for inverter duty.
If the non-inverter motor is used what are its chances
and limitations?
Many of you have really helped me out and I appreciate
the feedback. One other question and that is the old
style bubbler controls do they work under basically the
same principle as a VFD?
Wayne E. Lovison
service-parts@naglepumps.com
RE: Why must a motor be inverter duty for vari-speed applications?
I know these installations do not meet the recomendations from the drive and motor manufacturers, but we haven't had any trouble with them. Maybe we've just been very lucky.
Don(resqcapt19)
RE: Why must a motor be inverter duty for vari-speed applications?
Type in "adjustable speed drive" in the keyword search and it should bring it up.
RE: Why must a motor be inverter duty for vari-speed applications?
If you actually try to download this, it doesn't seem to be free anymore. Cost is $70. Or at least that is what happened to me.
dpc
RE: Why must a motor be inverter duty for vari-speed applications?
RE: Why must a motor be inverter duty for vari-speed applications?
Then I entered "adjustable speed drive" in the "keyword or phrase" box and clicked search. The first document that pops up is the Application Guide. Price is $0.00 (electronic copy), $70.00 (hardcopy). I click on the title as per the instructions under "Standards Search Tips". I scroll down the screen to "Complimentary Documents". There is the Application Guide, a Motor FAQ, and a Technical FAQ. Right-click on the Application Guide, save to your chosen location, and voila - free Application Guide.
RE: Why must a motor be inverter duty for vari-speed applications?
RE: Why must a motor be inverter duty for vari-speed applications?
Thanks, I got it. I guess this is why I do power engineering and not computer science
dpc
RE: Why must a motor be inverter duty for vari-speed applications?
an inverter duty motor should be use for all VFD on the market today. one main reason is that almost all modern VFD uses IGBT which switches from zero to peak in microseconds...the fast voltage rise (dv/dt) per unit time cannot be handled by a standard motor...inverter duty motors have more insulation on phase to phase or slot to slot..although you can technically use a standard motor premature breakdown is likely to happen...and for few extra money why not go to the right motor for the job reducing downtime and labor of replacing it on the job site.
dydt
RE: Why must a motor be inverter duty for vari-speed applications?
There are lots of applications where using a standard motor is possible wihtout risk. See the NEMA application guide for dealing with the voltage transient problem.
Using an inverter duty motor in can also cause some problems:
Availabilty
Additional cabling an protection for the fan
Cost (of course, but it's not the most important aspect)
Spare part inventory
Upgrading existing DOL drives with VFDs gets much more expensive, if the motor has to be replaced
And additionaly: If the voltage transient problem is the only reason for using an inverter rated motor alternative solutions, like a dv/dt filter should be considered. dv/dt can cause other problems than motor insulation failure, e.g. if small drives are used with long motor lines, dv/dt can cause current spikes. These spikes might trip the internal short circuit protection of the drive. In this case the dv/dt filter solves both problems associated with dv/dt whereas the inverter duty motos solves only one.
It would be nice if GordS could give furhter details of the application where the problem with standard motors on IGBT VFDs occured.
RE: Why must a motor be inverter duty for vari-speed applications?
Twowire
RE: Why must a motor be inverter duty for vari-speed applications?
Using a standard motor with inverters will cause overheating due to low cooling but that is compensated if you use a motor of higher rating which will have a larger surface area for cooling. But another problem arises is of the heating caused due to the 5th harmonic produced by the inverters. But new IGBT based inverters produce less 5th harmonic than their non IGBT based inverters. So its a question if whether you are trying to buy a new motor. If the answer is yes than go for the inverter duty motor. If you have the motor already installed try to decrease the load if you can.
kassad
RE: Why must a motor be inverter duty for vari-speed applications?
5th harmonic on the output side has alrady been elimiated with sine-modulated PWM-inverters using bipolar power transistors, Mosfets, force commutated thyristors or GTOs before the IGBT appeared on the market. I do not the exact date, but I guess the first inverters using this modulation technique was built nearly 25 years ago.
But, thats true, the IGBT was the power semiconductor which made VFDs to a product widely used in industry.
RE: Why must a motor be inverter duty for vari-speed applications?
Thanx for the tip. I was measuring it in terms of industrial acceptance.