changing from slipring motor to cage motor
changing from slipring motor to cage motor
(OP)
i want to replace a 300 hp slip ring motor to a 250 kw 333 hp induction motor with a kl16 rotor (high torque application).
will it work?
will it work?
RE: changing from slipring motor to cage motor
1. Is it started through a variable resistance in the rotor circuit? If so, see how fast is the external resistance brought down to zero. Is it pretty slow, that we cannot compare it with starting with a shorted rotor?
2. If (1) above is true, then is such a starting needed for the application?
If answers (1) or (2) above are negative, most probably, you could go for an induction motor, with proper ratings.
Narayanan UM
umn@ieee.org
RE: changing from slipring motor to cage motor
I think it will be very useful if you determine what kind a driving application is yours. If your system is using the advantages of slipring (such as soft starting or a limited speed control maybe?), you cannot change your motor directly. High motor starting torques sometimes can break the mechanical system with large inertia. A slipring is a simple way to limit this torque. If you make a change with cage motor you may have to use an additional power electronics soft starter also.
regards
RE: changing from slipring motor to cage motor
supply.In some cases there is nothing to beat a slipring motor especially
when starting a very heavy load where you want to limit torque and current
draw.My personal experience with them is on rubber mills.
RE: changing from slipring motor to cage motor
1.please check that your system should be very powerful to sustain starting current of motor.
2. I recomend that you should use atleast 4 stage auto-transformer method of starting to reduce starting current and smoother running.
The Cage motor can be run,in place of Slipring motor if the above suggestions applied.
Regards
khalid khan