I recommend Delta/Star also.
A few more reasons that rcwilson could have mentioned.
If you feed a star primary you must either have the generator windings connected in star or use an artificial neutral. The neutral can not be left floating on a Star/Star transformer bank. You must also run neutral conductors of sufficient capacity to withstand ground fault currents.
You may feed a Delta primary with either Star connected or Delta connected generators. No neutral connection is needed for the delta transformers.
Load sharing;
With Star/Star transformers, a fault current or unbalanced current on one phase will be carried on one winding of a star connected generator.
With a Delta/Star transformer bank, Unbalanced or single phase loads will be distributed across all three windings.
That is, a single phase load on "A" phase of the Star secondary will be supplied by all three phases of the generator.
"A" phase of the generator will supply part of the current and "B" an "C" phases will supply part of the current.
"B" and "C" phases on a Delta generator may be considered as an Open Delta connection. The open side of the Open Delta may be regarded as a Virtual single phase winding in parallel with "A" phase.
You have the effect of two single phase windings in parallel, sharing the current.
Ground fault currents on the secondary will be manifest as phase to phase currents on the primary. Primary phase tripping on a secondary ground fault will depend on your coordination settings.
I agree with rcwilson, use a Delta/Star transformer connection.
respectfully