Heavy oil AST heating

Heavy oil AST heating

Heavy oil AST heating

(OP)
I have a question regarding heavy oil tank heating.  I am looking into ways to keep oil products stored in large AST's (200M barrel or so) warm in cool climates.  I have seen internal steam coils, but are there other ways to do it?  External plate heat exchanger skid with pump recirculation?  
The site I'm looking into has steam available as a heat source, so I don't need electric or fired units.


Thanks
Replies continue below

Recommended for you

RE: Heavy oil AST heating

Your external exchanger would require that the oil always be warm enough to actually circulate it to the exterior exchanger.  The advantage of internal coils is that the oil can get cold in place and be warmed in place when you need it.

Exterior exchangers would require ALWAYS running at cool temperatures, maybe a 99.99 Fail-Safe design, which would probably mean 2 standby units.  If the oil ever set up in the tank it would be a hell of a job getting it moving to the external exchangers again.  

   Going the Big Inch! worm
http://virtualpipeline.spaces.msn.com

RE: Heavy oil AST heating

(OP)
Good point, but probably would have more than 1 unit to service the tank anyway.  Don't think I could get away with only one since that is a LOT of oil to heat.
With internal coils, many tank penetrations are required (depending on the # of coils required, maybye 20-30), so I'm trying to compare the cost of retrofitting existing tanks with coils (multiple nozzles) versus external exchanger(s),which would require only a few new nozzles.

RE: Heavy oil AST heating

However many units you need for minimum heat requirements, multiply them by the standby/outage risk increase factor.  

With an internal system, you could shut it down and let the oil set up until needed.  With an external system, it must be turned on well before cool weather approaches and left on until ambient temperatures are not in danger of falling again.  Sounds energy and maintenance intensive.  Be careful with a system like that.  Could turn into a white elephant.

   Going the Big Inch! worm
http://virtualpipeline.spaces.msn.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close