Avg.hood face velocity from duct velocity
Avg.hood face velocity from duct velocity
(OP)
I was asked to check the average face velocity of a canopy hood. It's located in a very user unfriendly location, but I can measure the duct velocity down stream 5' from the hood with easy. Duct dia is 4", average vel. is 921 ft/min and the hood measures 48" x 54". I beleive thats 80 cubic ft/min. Can I get a fair assessment of the average face velocity from these measurements or will I have to learn to rappel. Thank you.
RE: Avg.hood face velocity from duct velocity
Hood area = 18 ft^2
Hood face velocity = Q / A
= 80 / 18
= 4.5 fpm
This is VERY VERY low.... are you sure you are accurately measuring the velocity in the duct? Are your units correct?