Loading for bowling alley on 2nd floor?

Loading for bowling alley on 2nd floor?

Loading for bowling alley on 2nd floor?

(OP)
I got a project with a bowling alley on a second floor. Any ideas on loading?

Form equipment catalog I found on line, load is about 100 psf but instalation requires use of forklift.

Thanks.

Mike.

RE: Loading for bowling alley on 2nd floor?

Call the bowling equipment manufacturer and ask them what size forklift is typically used for installation.  Design the floor for that.  Be sure to post the forklift load on the drawing so the contractor can be notified what size to use.

RE: Loading for bowling alley on 2nd floor?

Does that cause noise problems on the adjacent floors, I wonder?

RE: Loading for bowling alley on 2nd floor?

(OP)
Well, I will call to manufacturer, when owner tells me name of it. Thanks for "not on drawing". I did not think of it.

And about noise problem, on the first floor is casino with slots and music and noise but itself.

Thanks.

RE: Loading for bowling alley on 2nd floor?

The IBC 2000 table 1607.1 point 7 lists bowling alley as 75 psf.  I would guess the equipment is localized and more of a maximum.  However, I do agree the forklift is the tricky scenario in this whole deal.  I would hope you are using a CIP system so you could get some good load sharing properties.  

RE: Loading for bowling alley on 2nd floor?

whymrg,

Your main design criteria will be deflection. Have your clients given you deflection criteria. It is normally very stringent.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close