Breaking current >Making current ??????

Breaking current >Making current ??????

Breaking current >Making current ??????

(OP)
I am looking for an anwser to the great debate on which is the greater value of current, the making current or the breaking current with reguads to circuit breakers, and why?
We know that a circuit breaker must be able to make on to a fault ( close) just in case the fault is not cleared, Hence the making current must be at lest equal to the breaking fault current. Please can someone  explain the  answer to the question.
Paul.
Replies continue below

Recommended for you

RE: Breaking current >Making current ??????

Making current is higher than breaking current.  When a fault occurs it decreases over the first several cycles.  So when a breaker closes onto a cycle it is at the begining of the fault when current is highest.  But when it comes to breaking a fault, usually breakers have a small delay of several cycles, so the fault has  started to decay, so it needs to interupt less current than it makes.  So the required making current is higher than the required breaking current.  

RE: Breaking current >Making current ??????

First you need to define what type of circuit breaker you are discussing.

For example for molded case breakers (taken form NEMA AB 1-1986,
"For AC, the short circuit making capacity of a circuit breaker shall not be less than its rated short-circuit breaking capacity, multiplied by the factor 'n' of Table 2-1... A rated short-circuit breaking capacity requires that the circuit breaker shall be able to break any value of current up to and including the value corresponding to that rated value..."

               Abbreviated Table 2-1
Rated Short                              Minimum required
circuit breaking                         making capacity  
Icu (amperes)          Power Factor           n x Icu
-----------------------------------------------------------
0-10,000                    .50             1.7 x Icu
10,001 - 20,000             .30             2.0 x Icu
20,001 - and up             .20             2.2 x Icu

RE: Breaking current >Making current ??????

Make current is greater than the break current.
Note the difference:

Make current is considered as the peak assymetrical value of the fault current and is measured at 10ms (first half cycle) after the fault onset.

Break current is considered as the rms assymetrical value and is measured in the region of 5 cycles (100ms). This is the region the circuit breakers operate. Some level, but low, of dc component is still present.

General practical rule for the calculation:

We calculate the rms value of fault current (If) at the onset of it (t=0sec), using subtransient values of reactances for the sources and taking no account of the dc component.

Then,

the make current is : 2.55*If
and break current is : 1.255*If

with dc component included in both cases.

RE: Breaking current >Making current ??????

If I understand the question to be related to the capability of the breaker, then I agree with everyone else - the breaker is capable of closing into higher currents than it is capable of interrupting.  When "breaking", the breaker must be capable of extinquishing the arc and withstanding the transient recovery voltage.  The worst case is for highly reactive loads when the current and voltage are badly out of phase.

ANSI standards for medium and high voltage breakers require a higher "close and latch" rating than interrupting rating.

dpc

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close