I think there is a little confusion here. Is the standard +- 10% or +-5%. My experience is with off load tap changers, but we purchase +- 5% as described by electricpete and haven't ever needed a larger range. But for your case the range you require is going to depend on the level of swings present in your system, buying the reduced range could save a small amount in the short run, but could be a large problem if you require the tap in the future for regulation.
Adding the taps which increase the secondary voltage are more more expensive because they add turns to your secondary winding for the secondary tap changer, so you could possibly use +7.5% -10% to save some cost. (Reduced MVA at lower taps)