How to choose the rating of a power transformer 11/0.400 kV.
Is it to be chosen based on the total connected load to the transformer or their are other factors to be considered.
This transformer is used to supply loads inside a hospital.

RE: Power Transformer Rating Selection

Other factors that might be considered include:

Impedance => impact on voltage under varying load conditions including motor starting.

Impedance => impact on short circuit current availability

future load growth? emergency overload in event of contingency (failure of alternate transformer)

RE: Power Transformer Rating Selection

Additionally, depending on where the transformer is located and the size, you may want to consider a dry type or using one of the new environmentally friendly liguids.

wbd

RE: Power Transformer Rating Selection

(OP)
Let me ask the question in another way,
Is the minimum transformer rating to be chosen equal to the total connected load (no diversity or maximum demand considered).

RE: Power Transformer Rating Selection

There is no simple answer because it depends on the nature of the loads, the application, economics and other factors.  For industrial applications, I would size the transformer such that its maximum forced-cooled rating is slightly larger than the highest peak demand expected.  Plus whatever allowance is appropriate for future growth.

For a hospital I would be more conservative and probably size based on connected load unless this was clearly unreasonable.  As a minimum, I would size such that the transformer could carry the maximum expected peak load continuously at its self-cooled rating - no reliance on fans.  



Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper – Data Security and Know-How Protection
Our data is constantly exposed to the danger of being intercepted or stolen as it wends its way over global data networks. Data security measures and measures for protecting intellectual property should not, however, first be implemented when data is exchanged – companies must lay the foundation for these measures within their own organization. Download Now
White Paper – Collaboration in the PLM Context
The influence exerted by the Internet of Things (IoT) means that there is a steadily growing need for collaboration in industry. Partners from new industries and areas of application need to be integrated in cross-company business processes to ensure that the lifecycle of smart, connected products can be managed from end to end. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close