Sub-Driveway Infiltration Bed

Sub-Driveway Infiltration Bed

Sub-Driveway Infiltration Bed

(OP)
I'm designing an infiltration area below a large, looped driveway area so that the post-developed 10-year flow will equal the pre-developed 2-year flow.  

I am placing two inlets in the driveway area so stormwater can flow into the infiltration bed more quickly, rather than just seeping through the ground surface.  I tried to model the system as follows: subcatchment to catch basin (with 2 grates as my primary outlets and a broad-crested weir to represent overland flow as my secondary outlet) to an infiltration bed, where infiltration is the only outlet.  

I keep getting an error message because infiltration is my final outlet and no calculations are completed.  Even when I add a "dummy" outlet (1" diameter orifice) from my infiltration bed, all the flow goes through the dummy outlet.

Another issue with this system is using the broad-crested weir to model the runoff that does not flow into the infiltration system.  Is there a better way to quantify this flow?  This is the flow rate I need to show that the SWM system meets the 10-year to 2-year requirement.

Can anyone out there help me figure out how to model this so I won't get any error or warning messages?

RE: Sub-Driveway Infiltration Bed

I am a bit confused by your description.  You have 2 drainage inlets but you say you are modeling them as outlets?  Outlets from what?  Same question for the weir...outlet from what?

Is this underground infiltration or an infiltration basin?

Have you defined an Exfiltration device on Outlets tab of your storage?

RE: Sub-Driveway Infiltration Bed

(OP)
My apologies for the confusion.  

The infiltration bed is below the driveway (about a foot underground).  The inlets serve as openings so water that is above the ground can get into the infiltration bed faster than it would if it were to just seep through the driveway.  

One of the main problems I am having in modeling this is how to quantify the flow rate of water that does not flow into the infiltration system; the stormwater that just bypasses the inlets and continues to flow down the hill.  That's where the broad-crested weir came into play, but using that seems to be a really inaccurate way to find the flow rate of excess runoff.  

And yes, I defined exfiltration as a device in my Outlets tab.  However, whenever exfiltration is the only outlet in a system, I get an error message and no calculations are made.

RE: Sub-Driveway Infiltration Bed

It sounds like you may need to determine your inflow using other methods such as HEC-22 type inlet capture computations if you do not believe you will capture 100% of the flow from the drainage area.

The exfiltration is another matter.  What is the error message?  Be sure to check how your elevations are setup in the Exfiltration device, and the "Allow Exfiltration" option.

RE: Sub-Driveway Infiltration Bed

As an aside:  If you were anticipating water seeping through the driveway, am I to assume the drive is not paved?

Are you providing any pretreatment of the runoff before it enters the underground system?  If not, it sounds like you are setting it up to fail when the underground storage clogs from sediment.

RE: Sub-Driveway Infiltration Bed

The key to modeling these situations is to have a clear definition for your pond.  Then you can determine how to define the storage and outlet control(s).  Remember that HydroCAD deals only with outlet controls.  Any inlet controls would need to be modeled as outlets on another upstream "pond".

ONE APPROACH to your situation would be model a below-ground pond, with exfiltration and overflow outlets.  This assumes that all the flow enters the "pond", but allows some of it to overflow if the level is high enough.

To define your storage, select an appropriate shape for the underground volume, setting the correct voids for the stone.  To enhance the storage, you can embed storage chambers, pipes, or other open volumes in the stone.  You should also define the above-grade storage that would be occupied if the stone overfills.  This might be a parking lot that can fill to the curb level.  Anything that would be part of the same level-pool can properly be included.

Then create an exfiltration outlet for the below grade outflow.  This can be based on your choice of wetted area, surface area, or constant flow.  To model any overflow, you could use a weir or other device.

In this scenario, the entrance grates don't appear in the model at all, since we're assuming that they are able to pass all the runoff into the pond without diverting any flow.  However, if the inflow exceeds the storage and exfiltration capacity and the level rises above the overflow device, the flow will be correctly split between the exfiltration and overflow outlets.

For further details and illustrations please see www.hydrocad.net/exfilt.htm

RE: Sub-Driveway Infiltration Bed

PS:  If you're getting any error messages, please click the help button for a detailed explanation.  You will find answers to 99% of all problems in the linked help system.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close