Bentonite Cement Water ratio for Inclinometer in soft to firm clay
Bentonite Cement Water ratio for Inclinometer in soft to firm clay
(OP)
I have specified an inclinometer to be installed in an embankment reservoir for monitoring lateral movement.
The borehole for the inclinometer shows soft to firm clay (say 45kPa).
I have asked the contractor to grout up the inclinometer with a bentonite / cement ratio of 2.5:1, which will be placed using a grouting pan.
The contractor used the following mix 2.5kg bentonite to 1kg of cement to 80 litres of water.
My personal feeling is that this mix will not give me a shear strength of 45kPa infact Id be surprised if it sets at all.
Ive been looking for design data for grout mixs but its proving difficult to find. Any advice would be appreciated.
The borehole for the inclinometer shows soft to firm clay (say 45kPa).
I have asked the contractor to grout up the inclinometer with a bentonite / cement ratio of 2.5:1, which will be placed using a grouting pan.
The contractor used the following mix 2.5kg bentonite to 1kg of cement to 80 litres of water.
My personal feeling is that this mix will not give me a shear strength of 45kPa infact Id be surprised if it sets at all.
Ive been looking for design data for grout mixs but its proving difficult to find. Any advice would be appreciated.
RE: Bentonite Cement Water ratio for Inclinometer in soft to firm clay
RE: Bentonite Cement Water ratio for Inclinometer in soft to firm clay
1:2.5:0.3 and 1:6.6:0.4. You can find the page at
http
RE: Bentonite Cement Water ratio for Inclinometer in soft to firm clay
My other concern is that the mix only uses a bentonite cement ratio of about 0.4 : 1.
I would be interesested in mixes using less water and more bentonite to try and match the deformation modulus of the clay.
RE: Bentonite Cement Water ratio for Inclinometer in soft to firm clay
RE: Bentonite Cement Water ratio for Inclinometer in soft to firm clay
RE: Bentonite Cement Water ratio for Inclinometer in soft to firm clay
Something we do alot is drill as small of a hole as possible (4"in dia. for 2 3/4") casing and use the grout valve that Slope Indicator sells. With the smaller annulus the grout mix becomes less critical.
Could you please clarify your last question, are you refering to not installing an inclinomenter an using something like a TDR cable instead?
RE: Bentonite Cement Water ratio for Inclinometer in soft to firm clay
RE: Bentonite Cement Water ratio for Inclinometer in soft to firm clay