Flywheel
Flywheel
(OP)
Is there a practical limit to a flywheel size in inertia, lb-ft^2 or kg-m^2 on a 500 HP, 480 V, 1800 rpm motor. I would like as big as I can have. For 60 Hz starting, the heat on starting will limit the size and that may be the value listed in Nema MG1. However, if started on a vfd it could be ramped up slowly.
RE: Flywheel
You would also need to worry about windage and bearing friction as your flywheel got bigger.
As for the motor, with a VSD I can't see any problem as long as the previous are considered.
RE: Flywheel
Using a VFD results in the motor never operating under high slip conditions and so the thermal mass of the rotor becomes irelevant. Check with the VFD manufacturer to ensure that the VFD is capable of controlling the heavy load.
Mark Empson
http://www.lmphotonics.com
RE: Flywheel
RE: Flywheel
For starting of an unloaded induction motor DOL, the total rotor heating energy is not only proportional to the kinetic energy of the rotor, it is exactly equal to the final kinetic energy of the rotor. There's no obvious physical reason for this, but can be shown mathematicaly.
If you add a load to the motor, then this heating is increased by a quantity which resembles the average value of Te/(Te-Tm). This factor can get quite large if Tm (load torque) approaches Te (motor torque) for the same speed. A very interesting result is that the total rotor heating energy will increase dramatically if you use a reduced-voltage start. This runs a little bit against our intuition which suggests that a reduced voltage start is less stressful for the motor. Reduced voltage starting actually generates more heating in both the rotor and stator, although the heating is spread out over longer period of time.
You're right that VSD applied properly will solve all of these problems.
RE: Flywheel
Please, what is this actually needed for?
RE: Flywheel