ASTM D 4253: 90% or 95%?
ASTM D 4253: 90% or 95%?
(OP)
I am considering buying the test set for the 4253 procedure (laboratory vibratory compaction) so that I can perform field density test on 3" minus soils that have an aboundance of aggregate retained on the 3/4" sieve (say 50 to 70 percent retained 3/4" sieve). Once I find the maximum density in the lab via ASTM 4253, do I specify 90% or 95% of that number in the field when the contractor is trying to compact it under a future structure? Is 4253 equivalent to ASTM D 1557 (if I ask for 95% of 1557 should I ask for 95% of 4253?)





RE: ASTM D 4253: 90% or 95%?
I would suggest a criteria based on SPT borings with a minimum N value instead of compaction.
RE: ASTM D 4253: 90% or 95%?
RE: ASTM D 4253: 90% or 95%?
RE: ASTM D 4253: 90% or 95%?
showing 4253 gives you lower maximum desities than other methods. This is what I recall also. So you may want to increase your field percentage density requirement.
RE: ASTM D 4253: 90% or 95%?
The thread below discusses a little about what you're talking about. See if this shows up:
thread261-37564
To make a long story short, in my testing I've found that the maximum density attained with ASTM 1557 is approximately equivalent to ASTM 4253 vibratory table test. Therefore, if you want 95% of the 1557, I would go with 95% of the 4253. Caveat: My testing generally included SA-SR fine to medium sandy soil with little silt content (<3% by mass) a small amount of coarse sand, and no substantial gravel content.
I've seen similar testing results that show the same thing as CarlB describes, hence my caveat noted above. Gradation and particle shape make very big differences in what type of compaction test will yield higher values-ASTM 4253 vs. ASTM 1557, for example. Also refer to ASTM STP 529(?). If I find that number is incorrect, I'll let you know the correct STP #.
In terms of testing, I agree with dmoler that you'll have trouble with a nuke gauge. I agree with BigH that SPT is not the way to go too. BigH also alluded to a "means and methods" specification for compaction, which could be valid for part of the testing program. If you need some additional quantitative results of the compaction, a larger scale "lined pit" test as BigH offered, is probably a good way to go if you need to use this particular gradation as engineered fill.
RE: ASTM D 4253: 90% or 95%?
RE: ASTM D 4253: 90% or 95%?
Since sampling of the geomaterial is not needed, only to determine if the placed and compacted fill will support the structure, why not use the SPT for that purpose, as long as the rock is not too big. I have done verification with similar projects with max aggregate of 1.5". I also had the fill sampled and it must pass a classification requirement(SP, ect.) with max aggregate size.
I really perfer the method that BigH mentioned above (# of passes correlated to density) but the only problem with that (maybe not a problem if someone pays for this) is a person has to stay at the site to monitor and verify construction in accordance with this. If they call after everything is done (unfortunately a usual practice) then I have used the SPT approach.
Nothing is perfect in construction, nor goes according to plan.
RE: ASTM D 4253: 90% or 95%?
As an update to the previous thread dealing with how to laboratory test your oversize material, I did some looking around for field compaction verification references. USACOE seems to like doing test fills (or at least they did at one time) for rockfill placement. Unfortunately it seems that few, if any of the USACOE reference papers listed in the EM bibliographies on this subject are available electronically.