Not sure if this is the correct forum but here goes anyway.

We are about to take over the management, operation and maintenance of a new gas and distillate fuelled power station.  What are peoples experiences of the control of ignition sources on power plants? I have been on chemical plants and refineries where security takes all possible ignition sources from visitors before they enter the site - eg. mobile phones, matches, lighters, etc.

At the power plant there are similar hazardous areas but the degree of control until now seems more lax.
Replies continue below

Recommended for you

RE: Ignition sources on gas power plant


Consult your msds and look at the ignition temps. It is not a matter of laxity.

RE: Ignition sources on gas power plant

I have seen different people rate the same area differently.  We have natural gas compression stations and take a class 1 div 2 approach that all the gas should be in the pipe, unless something unusual has happened.

Correct me if I’m wrong here, but you have a power generator station with bi-fuel engines, diesel and natural gas.  What percentage of the station has the same rating as your chemical plant?  I would think that just the pump house for the diesel and the compressor for the NG would be the only areas close to similar to your chemical plant.  Who defines your rating code?  We have DOT codes which define what pressure pipe and what equipment gives a specific rating.  If applicable code says no ignition sources, then it means no ignition sources.  Make sure you know the code and apply it to your plant.  If you try to apply your old methods to the new plant, you may have rules which are stricter than the code requires, and your bean counters will wonder why it is so expensive to operate this plant.  For example, is all the wiring in the generator plant to the same codes as your chemical plant?  In essence I think you should be asking what the code requires, not what other people are doing.

Good luck, I hate management forced decisions that have no field experience.  Of course I hate explosions also, especially when I'm in the general vicinity.  I also dislike it when employee morale or plant explosions affect my stock prices.  Boy, I am a really disagreeable person tonight.  

 

dwedel
Hotrod Big Engines!
For site policies and guidelines
see FAQ731-376

RE: Ignition sources on gas power plant

I have done some hazardous area classifications for power stations recently, both Gas turbines and bi fuel boilers, such as yours.

Looking firstly at the gas side of things.  The gas in the custody transfer station has quite clear hazardous area guidelines, that will be similar to chemical plants.  These will not stop when the gas gets into the power station.

For the diesel.  I believe that a pressurised diesel line has the potential to create a mist and therefore has a hazardous area.

However, the power stations have generally had well defined hazardous areas or at least the installation was compliant.  To answer your question about whether you take ignition sources away from people - On the last few power plants I have been on I have had to carry a gas detector to allow me to take photographs.

RE: Ignition sources on gas power plant

I have seen some small personal gas detectors like Tickle talked about.  Those would be nice.

dwedel
Hotrod Big Engines!
For site policies and guidelines
see FAQ731-376

RE: Ignition sources on gas power plant

(OP)
Is a standard mobile phone / cell phone likely to ignite a natural gas leak?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close