I'm looking for standard design dry and wet bulb temperatures for Cairo, Egypt. I can't find anything on the net and I don't have access to any ASHRAE info. I'm getting wildly different numbers from suppliers quoting cooling coils. Can anyone offer any help?
TIA,
djv
TIA,
djv
RE: cairo design conditions
0.4% cooling is 100 F with MWB of 69
1% is 97/69
2% is 95/69
RE: cairo design conditions
RE: cairo design conditions
Just in case MintJulep is done for the day --
The % numbers represent the percent of annual hours during which the design condition (statistically) will be exceeded.
MWB is mean wetbulb coincident with that design dry bulb.
Good on ya,
Old Dave
RE: cairo design conditions
Mediterranean Coast. In recent years the humidity has spread to Cairo and the city swelters in
August. Winters are mild with some rain, but usually there are bright, sunny days and cold
nights.
There is a short spring and autumn and during the 50 days (khamseen) between the end of
March and mid-May, dust storms can occur sporadically.
for more go here:h
RE: cairo design conditions
The only problem I see is the selection of coil ADP if the above data is correct. I would settle with 1% conditions. I will also have a look at 1% values of WB and MDB for extra latent loads.
Regards,
RE: cairo design conditions
Do they give %data for WB as well? My application is cooling air for a plastic blown film line. I'd like to account for those hot and humid days, but I don't want a giant, expensive cooling coil. One supplier used 110DB/ 91 WB, another used 128DB/ 95 WB, another used 102 DB/ 76 WB. The latter seems most appropriate.
RE: cairo design conditions
We run into this often when it's process cooling. The MWB is an average of wet bulb temperatures that occur coincident with design dry bulb. That doesn't mean it won't hit the design dry bulb one day and rain at the same time, in which case you'll have less than the capacity you need to control humidity. If that's acceptable on occasion, then the 0.4% numbers or even the 1% numbers are OK. However, if loss of temperature control would be extremely expensive (say, cause the need for a process shutdown), you might size the unit up. It's a judgement call....
Let us know how it works out for you!
Old Dave
RE: cairo design conditions
Thanks. I understand that the MWB is the mean and that sometimes WB will be higher and I will have more latent heat to account for. If it is a small amount of the time, then ok, no big deal we just have to run a little slower. The percentages don't tell you how often that will be, just how often the DB will be above, correct?
What is one size up (ref my numbers above)? As I said, 102/76 seems reasonable. I will be pulling air from inside a factory, which is not air-conditioned, but is at least out of the sun. It can get warm though because of the processing equipment, so I figure that is a wash (i.e. inside temp same as outside temp).
RE: cairo design conditions
RE: cairo design conditions
The cooling is for the process. It is a blown film line. We want to supply 3500 CFM, 54F air to the outside of the bubble and 2000 CFM, 54F air to the inside of the bubble.
RE: cairo design conditions
The design condition for cooling can be based on either maximum dry bulb temperature with mean coincidental wet bulb temperature or maximum wet bulb temperature with mean coincindental dry bulb temperature. Your local weather data book can provide you these conditions. For tropical areas where humidity is a big problem, 1% values of WB and MDB can be a safe bet, when you see the total enthalpy that is to be removed by the cooling coil.
Total enthalpy for the above 3 design temperatures given by MintJulep is same but there is a significant difference in latent load. If WB is nearly constant over a span of one year(it looks like, from the above data), you will have high humidity problems if you choose 0.4% values. This can be as high as 99.6% of time(because for 99.6% days DB is less than 100F theoretically)
The latent load difference between the 1% and 2% values is not significant. So you can safely choose 1% values. If your area is highly humid then check for WB and MDB values to know the increase in total enthalpy. You need not worry if the total enthalpy at this design condition is nearer to the total enthalpy at 1% DB and MWB conditions.
Moisture problem will be predominant if you are pulling air from inside.
Plot all the design coil conditions on a psychrometric chart and also plot the actual design values given by MintJulep. Select those coil conditions which can take care of higher hmidity ratio than the actual design values.
Regards,
RE: cairo design conditions
1% conditions: 23.77%RH, 33.23 BTU/lb
102/76: 30.76%RH, 39.6 BTU/lb
110/91: 48.86%RH, 57.58 BTU/lb
128/95: 30.71%RH, 63.41 BTU/lb
What do you think? It seems a big difference. Someone mentioned sizing the unit up from the 1% numbers. Well, would that be 1 ton, 5 tons, etc...? Any rule of thumb there?
I understand Cairo to have hot and dry summers, but you suggest pulling inside air may mean I pull more humid air, correct? The factory has very large doors each end, and open windows along the sides, so I don't know how much more humid it might be that the outside.
RE: cairo design conditions
Is it a once through system? I may be of little help as I am totally unaware of the production process your are speaking about. If it is for space cooling then I will consider around 1 ton for 400 cfm as a rough estimate.
Regards,
RE: cairo design conditions
Can you elaborate on the control valve? How do you determine the 50% value?
I appreciate the help. As I said I'm not an HVAC guy and haven't had too many air cooling projects yet in this job.
RE: cairo design conditions
What will the air condidtions be when it is done in the process? It may be more efficient to recycle the process air than go 100% OA.
RE: cairo design conditions
The air is around 180F after the process. Nobody recycles to my knowledge.
RE: cairo design conditions
Since the factory is not air conditioned, and if full of heat-producing equipment it will be hotter than the outside design conditions noted by ASHRAE on a design day.
You might actually be better off using outside air than air from inside.
RE: cairo design conditions
Unfortunately I don't know inside conditions and don't have time to wait 'till summer to collect data. I will use the 102/76 condition and start by taking inside air, and change to outside air if needed later. As long as the air inlet is not too close to the machinery, then I don't think the air will be hotter than outside air as the factory is somewhat open and ceiling is up to 60' tall in some areas, so there is plenty of place for the heat to go.
quark (or anyone),
Still curious about the comment that some of the coil conditions I mentioned are redundant and would put too much load on the control valves. In what way do are they redundant? In what way do they put too much load on the valve and how can this be known at this time without more detailed info on the valve and the system details?
RE: cairo design conditions
Just calculate total heat removed from the extruded parts by mCpdT where m is mass rate of components, Cp is specific heat and dT is temperature difference of initial and final conditions. I imagine potential savings by heat recovery from exhaust air.
No rocket science in the control valve thing. Fro ex. if you select the coil with 110/91, there is a heat flow of (57.58-22.8=) 34.78 btu/lb from air, where as you require to remove only (33.4-22.8=)10.6btu/lb. So you coil capacity is high by 300%. So the maximum flowrate should be not more than 30% of the maximum coil capacity.
Regards,
RE: cairo design conditions
Since it's a once-through system, the capacities won't go by thumb rule of 400 cfm to a ton. You may have to do a proper load calculation to find this out. You also have to take into consideration any heat generation from your process. What kind of temperature and humidity conditions do you want to maintain ? You have indicated some air quantities in cfm. How was this arrived ?
Depending upon how critical your process is, you may choose 100/69 or 97/69 or 95/69. Are you planning a chilled water system or a DX system ? There are a few precautions to be taken if it's a DX system, especially for a once-through system.
HVAC68
RE: cairo design conditions
On the control valve, I got it now - I didn't understand that you were considering that 102/76 was the required condition.
quark/ HVAC68,
On the heat removal, we normally consider 1 ton per 50 lb/hr as a rule of thumb. At our production rate this is 32 tons. Calculating I get a similar number (BTW, you have to also consider the phase change - liquid to solid). Problem is the aerodynamics of blown film bubble cooling is very complicated and cooling efficiency is very sensitive to equipment design, air flow rate, and air flow pattern as it's adjusted by operators.
The internal air cfm comes from an analysis on the die that shows it can handle a max of 2000 CFM. The 3500 CFM outside air comes from the machine OEM.
The problem is some of the quotes are from plastics industry OEM's and their chiller loads range from a bit higher than mine to much higher than mine. I'm still trying to get some answers, but in the meantime started this thread to narrow down an appropriate temp condition since they are all over the place on my quotes. When I get some answers to my questions on the quotes I will go back to the machine OEM (they are not quoting this cooling modification) and get their opinion on the best system, considering their equipment design.
You've all been a great help. Thanks a lot.