kryanl
Mechanical
- Jul 30, 2001
- 34
I've been trying to go through the sizing of vents for a couple fuel oil storage tanks, and have come to a standstill when trying to find both the latent heat of vaporization and the molecular weight of fuel oil. I am looking into No.2 oil through No.6. (We're renovating a small tank farm.) Actually, I do have some numbers for each of the properties, but when I run through the calculations for emergency vent sizing, I come up with vents that are much smaller than what are on the existing tanks that we are replacing. I suppose back in the day, there had been different method of sizing vents. But, I'd been hoping that I was using the wrong numbers. Can anyone please help straighten me out with correct LHVap and MW for basically each of the Fuel oils?
Thank you,
Kayla
PS. just to make sure, the equation I am using is:
CFH = V*(1337/L*sqrtMW)
where v is found from a table, L is the LHVap
Thank you,
Kayla
PS. just to make sure, the equation I am using is:
CFH = V*(1337/L*sqrtMW)
where v is found from a table, L is the LHVap